kendrickg
Member
Ok, first time poster on this forum. I checked the archives for a similar situation and found this. http://www.plctalk.net/qanda/showthread.php?t=12816
My situation is this: We are putting a 20 HP VFD on a large laboratory transportation shaker table. This table moves up and down with eccentric shafts driven by the motor. This motion causes the VFD to trip the bus overvolt fault. The table will run up to 20 hz, then trips. Watching the live bus voltage option on the drive i can see the voltage spike whenever the table is in the downward stroke, then it drops back when the table is one the upsroke.
Can i use a AB dynamic brake, for a 10 HP motor. They are rated at a 20% duty cycle. The thread i listed above about the fish mixer stated to use one about a 1/4 the size of the motor. But this shaker has a 8 x 10' platform and a payload of 8000lbs. Is this motion of an ecentric shaft with gravity helping some of the time a %50 duty cycle? The only other option i saw for %50 duty cycle at 20 HP is to use a brake chopper and a resistor pack, for a sum of about $3500. That is a bit too much.
Thanks for looking!
Specs
L.A.B Transportation shaker with a 20 Hp 460 motor
AB 1336f plus II AC drive
Drive trips bus overvolt fault code above 20 hz
My situation is this: We are putting a 20 HP VFD on a large laboratory transportation shaker table. This table moves up and down with eccentric shafts driven by the motor. This motion causes the VFD to trip the bus overvolt fault. The table will run up to 20 hz, then trips. Watching the live bus voltage option on the drive i can see the voltage spike whenever the table is in the downward stroke, then it drops back when the table is one the upsroke.
Can i use a AB dynamic brake, for a 10 HP motor. They are rated at a 20% duty cycle. The thread i listed above about the fish mixer stated to use one about a 1/4 the size of the motor. But this shaker has a 8 x 10' platform and a payload of 8000lbs. Is this motion of an ecentric shaft with gravity helping some of the time a %50 duty cycle? The only other option i saw for %50 duty cycle at 20 HP is to use a brake chopper and a resistor pack, for a sum of about $3500. That is a bit too much.
Thanks for looking!
Specs
L.A.B Transportation shaker with a 20 Hp 460 motor
AB 1336f plus II AC drive
Drive trips bus overvolt fault code above 20 hz