I am learning PLCs and have a setup at work with a slc 5/01 processor. I am using a 1747-pic module and in rslinx node 0 is found. The problem is that it does not find my processor, any suggestions would be appreciated
So you have the 1747 PIC/AIC driver loaded and it's running without errors?
The Autobrowse box is checked in Linx?
If you are often switching between the DF1 driver, and the PIC driver, a good thing to do is close linx and delete the serial port from the device manager. Then scan for new hardware and windows will install it again. Then restart Linx. If you are using XP, you should see a screen that warns you that the driver is not a certified MS driver (in which you have to select "continue anyway").
The autobrowse is checked. running win 98. tried removing serial and reinstalling. get a diagnostic status failed 0x4 in rslogix. have also seen no response from processor at path/node.
Have you EVER communicated with this CPU? can you reset the processor and start from scratch? could the com port be configured for some other communication? if this is the case you will not be able to talk to it or see it.
have tried two different processors (both 5/01, mainly becaude thats all we have left available in the shop) and cant connect with either one. had one connected several months ago. i think i am just overlooking some small detail.