-=| Troubleshooting Modbus communications |=-

JuNGLisT

Member
Join Date
Sep 2003
Location
North Carolina
Posts
31
Having trouble with Modbus communication between AB SLC and GE Fanuc. We are using a O-Link M10 SLC mount adapter card for modbus comm. I need some help trying to communicate with O-link M10 adapter. Is there a software to use with laptop to see if the O-link is working properly? Or is there another way to troubleshoot out problem?
 
Last edited:
Wintech's Modscan32 (master) and Modsim32 (slave) modbus emulators may be of use on a laptop with a standard COM1 port and an adaptor to whatever protocol you're using (232, 485, etc). Not familiar with the OLink products.
 