Hi all. We have a customer looking to add some VFDs to a HVAC control system and they are requesting that all equipment be OPC compliant. We normally use Toshiba drives with the ETH200 module from ICC for Ethernet/IP comms (not OPC). Does anyone know of such an animal? Thanks.
 
It is only PC software that can be "OPC compliant", and it has to work on a Microsoft Windows PC.
Field devices such as i/o blocks, sensors and VFDs can be compatible with a bus standard such as Ethernet/IP.
You need to find an OPC server that can directly access field devices via Ethernet/IP.
 
Thanks JesperMP. You cleared up some of the confusion on our end. I even went to an OPC seminar and I'm still scratching my head.
 

Similar Topics

This is a little OT, but I know there are some experts here on the forum with the relevant experience. I have a project that expects a very long...
Replies
6
Views
1,081
This is a little OT, but I know there are some experts here on the forum with the relevant experience. I have a project that expects a very long...
Replies
4
Views
1,118
I have a project where the customer specs will not allow the use of the VFD's STO safety function. They demand dual safety contactors in front of...
Replies
18
Views
1,887
Hello guys, I need your help. The client has 3 vfds. My colleague noticed that when they ran them simultaneously, the vfds were having analog...
Replies
12
Views
2,351
Greetings experts, Can current transformers be used on the incoming mains (480, 3P) of a machine that has regenerative VFD's? Current...
Replies
9
Views
3,233
Back
Top Bottom