half
Member
The current system I am looking at has eight GE 90/70 PLCs networked together via Genius Bus Controllers (addresses 21-28). Additionally, there is an ELB 906 PCIM module (address 30) installed in a PC to provide the operator remote start/stop commands for the devices on the PLCs. As best I can tell the 8 PLCs and ELB share data via G type registers. I will be replacing the role of the PC/ELB module with a SCADA server. All logic with be retained in the PLCs.
So my question is how to I get my SCADA system to write/read G registers? More importantly, how can I do so while keeping the existing MMI operational until all PLCs can be tested on the new system and a complete cutover can be done.
My initial thought is to add a 90/70 PLC with a Genius Bus Controller on the network and give the GBC an address of 31. It is my understanding that I’d be able to talk from the SCADA server directly to the CPU via Modbus. Then I can program the GBC on this rack identical to the programming on the ELB except give it an address of 31. Then when the PLC is turned on it would take over primary control of the bus and the ELB would have backup control. At the end of the day I could just turn the PLC off and the ELB would take over. When testing is completely done then the ELB can be taken off the network.
Is this correct?
Anything I am missing?
Is there a better solution than adding a 90/70 PLC to the network?
Any potential problems with talking Modbus direct with a 90/70 CPU?