Hello,

I can´t to link controller L55 with RSLgix5000 v.16.

The RSLogix show me the next error Error: Rung 0: Empty rung

Please, if somebody can help me.

Thanks.
 
Ok, the channel is RS-232 and RSlinx 2.43.01.23, the RSlinx see the controller, but RSlogix5000 can´t.

I Upgraded the firmware of the controller for the RSLogix5000 v.16.

Thanks.
 
I'm not sure that this IS the problem, but having an empty rung is not accepted in Logix5000!

Try to open the file with the empty rung ad delete that rung, then try to down load again. I'm guessing that your system doesn't get past compiling, and therefore does not proceed to the download section.

Michal Rudbeck-Rønne
M2R
 
I do belive if you upgrade the firmware you automaticly blow away the program hopefully your program was writing in version 16. Clear the processor memory and download the program
 
Thank You,

But, I was in error, because I have the demo version RSLogix. That explains everything.

Thanks again
 
No, having a demo version has nothing to do with an "empty rung" error message.

Michal_dk was correct.

That error message occurs when you are trying to compile a program for download. It occurs when you have an empty rung with no instructions on it. You will find an empty rung at the top of one of your ladder files.
 
You get the empty rung when you first open a subroutine that is empty. The program automatically inserts a rung for you to start your logic on.
Regards Alan
 

Similar Topics

Hi, I want to exchange data between two L55 PLCs using ENBT PLC1 is the main PLC and consist of 1756- CNB, L55 CPU and ENBT. Five remote I/O racks...
Replies
7
Views
1,028
Hi, Anyone can help to get the FW16 for 1756-L55 as the CPU OK indication is flashing red as I have a new CPU and inserted a memory module. While...
Replies
9
Views
1,707
Hi, I just bought a new control logix 1756-L55 from a supplier in UK. The Red indication is showing stable and as per the manual its showing CPU...
Replies
7
Views
1,825
Hi, I have a CPU with 1756-L55, Which version of RSlogix5000 is to be used as I have version 20 and its not supporting. I tried to install...
Replies
4
Views
1,375
Hi all, Any experience of the above? Happened 3 times now in 1.5 months. Processor is about 10 years old, software major revision is 19...
Replies
9
Views
5,545
Back
Top Bottom