We have

2 X S7 417H Prcessors on two racks set up for redundancy
2 X CP443-1 communications modules (1 on each rack)

When we power up the left hand power supply the whole rack gets powered up i.e. both plc's and both comms modules. All the LEDs on the processors come on and the comms modules look more or less normal. If the right hand power supply gets powered up on its own all the LEDs on all the modules flash. We have set up this configuration before and have never seen this situation.

We have swapped the power supplies but the symptoms remain the same.

Starting to think rack problems.

Any ideas guys ??

Barry
 
Just an update

We left out the right hand power supply and both processors seem to power up normally ??

When we set up this configuration before (on another project) I seem to remember that each power supply fed each individual processor.

Barry
 
We are trying to use both racks. It just seems strange that both racks get powered by one supply.

This unit was supplied to us by the client to do FAT (Factory acceptance testing) for a project that is replacing an old AB PLC2 system. I think it is a second hand unit that has been superceded.

We have asked the client for a replacement rack so we will see how we go.

Barry
 

Similar Topics

I have a linux server (on prosumer hardware), debian stretch 10. There was some utility works in my area and they hit the power line. The server...
Replies
15
Views
3,198
My attempt to communicate with Foundation Fieldbus transmitters with Pactware and a new, out-of-the-box Softing FF modem are a disaster - failure...
Replies
17
Views
5,015
I'm looking to create my own 'screen saver' screen on a PV800 and I cannot find a tag thats suitable to read back in the PLC that i can then write...
Replies
4
Views
2,925
Hi Guys I'm trying to scale an Analog input. The manual talks about comparing the analog to a data table to result as another device. Function...
Replies
3
Views
2,097
Hi I would like to know if you can suggest a solution to a problem. I have a piece of machinery that is primarily pneumatic in its operation and...
Replies
8
Views
1,854
Back
Top Bottom