Hello Steve_D;
In the plants we are commissioning the client has the same requirements for our process valves and flowmeters. These do not have sub-D 9-pin interface for Profibus-DP, only screw terminals, and the client felt we had to provide a way for him to service the equipment without affecting the network.
We are using Weidmuller T-connectors for Profibus-DP, models 8714260000 and 8714240000 (this last with integrated terminator, externally powered, 24 V. To make sure we have as little effect as possible on network stability, we specify max. length of the spurlines to be 20 cm each (some Profibus documentations specify a maximum total length of all spurlines at 1,5 MB to not exceed 6 m; we try to remain as far from that limit as possible). The esiest way to ensure that is to install the T-connector on the pipe wue use to bring power to the equipment, very near the gland entrance for the network connection.
At 1,5 MB, we have yet to have a major problem with this setup, and we are finishing our 22nd plant over 3 years as we speak.
Hope this helps,
Daniel Chartier