TI Power Supply

Mostly

Member
Join Date
Jun 2005
Location
Colorado
Posts
13
Anyone out there have a print for the pin outs on a model 500-2151A power supply for a TI plc? Any kind of documentation on the rack would also be helpful. I'm trying to verify a bad power supply before I send it in for repair.
Just want to make sure this is the problem and not some other issue with the rack. I have pulled all cards from rack, removing any load the power supply should see. Still no 'DC ok" light.

Fuse in ps checks ok.

Thanks for your help

Mostly....sometimes
 
Hi, I've no details such as you request but from what you've written there would appear to be two symptoms in agreement: the PSU is not working; and the "DC good" LED is extinguished. How much more evidence do you need before you agree that this PSU is in need of repair or replacement?

My memory of the 500-series is that it was pretty robust stuff not given to many false negatives. There are no direct AC connections to the PSU (terminals on the mounting rack) and all the DC output goes through the backplane via card-edge connectors. How do you propose to test it accurately?

Regards

Ken
 
Ken,

I was planning on testing it out of the rack to verify the rack is not the problem. I have unplugged all cards from the system, so I'm confident it is not a card pulling down the ps.

I have seen this happen before where a screw had gotten behind a rack and caused power supply issues.

Thanks for the reply.
 

Similar Topics

I have the power supply in the link below. If we want a breaker to isolate and protect the input side how would I size that correctly being 120...
Replies
8
Views
195
I am looking for power supply that I can mount on vertical DIN rail, and when mount that way is =< 4" wide. this is what I have now.... this is...
Replies
21
Views
575
I have Rhino 120 to 24 dc power supply and it has 2 Positive and 2 negative terminals on the DC side but no ground terminal. Should I connect one...
Replies
9
Views
433
We've still got a ton a PLC 5's installed and running. We lost a 1771-P7 Series B power supply. There are a lot of 1771-P7 series D power...
Replies
3
Views
231
Long ago, it was often a customer spec to always use a transformer for isolation of the control circuit from the rest of the equipment. For 24vdc...
Replies
5
Views
671
Back
Top Bottom