Hi folks , now we had a project were we had to install a micromaster 440 , this drives are to be controlled by an external 4 to 20 Ma form a PID conroller the process variable input to the PId conroller is Flow measurement , the process is such that when the flow is lower the set point the VSD reduces speed and vise vasa . we have set the P value to 70 I to 5 and D to Zero but , whenever the VSD is started it trips immediately as the controller output Ramps up very first and not stable . could any one help and come out of this please any suggestions are welcome.
 
Hi Robert,
Note the MicroMasters disable the normal ramps when PID is enabled. Instead it uses P2293 to achieve ramp. Also I suggest using something greater then zero on the minimum (anything greater than 0.0 even 0.1) their was a bug in some of the older firmware versions.

mm440_1.JPG
 

Similar Topics

What is the meaning of F009 fault in Micro Master MM440 drive. We are not able find this fault in the operating Manual Mani
Replies
0
Views
2,794
I successfully got a Micro 820 (Slave) and Red Lion HMI (Master) to work together using Modbus TCP. But now I need to add an Automation Direct...
Replies
3
Views
2,643
Hello Guys, I have two different Micro 830 PLCs, namely 2080-LC30-100QWB and other one is 24AWB. I want to make one Micro 830 as Modbus Slave and...
Replies
1
Views
2,557
replacing this drive is the program and parameters in the saved in the front module it is using profibus for its coms
Replies
6
Views
1,532
Does any actually use Starter and think its any good ?! It takes 4 hours to install on a normal laptop, takes 10 minutes to start up, wont run...
Replies
5
Views
2,275
Back
Top Bottom