micrologix 1500 communication problem

phish13

Member
Join Date
Oct 2007
Location
Ontario
Posts
6
I don't know if I'm missing something. I can identify the plc and bring it up no problem. But when I try to go online it begins uploading and then gives a bad communication fault. using df1 autoconfig with rs linx and serial to front port cable.

Thanks for any advice.
 
I'm not sure I get the whole picture, how do you mean you can bring it up?

I guess that looking in RSLinx you can see the CPU of the ML.

Du you have the program that is in the CPU?
If so, are you using Systems communications to find the CPU before going online?

Make sure that when going online it is the actual program that you have, RSLogix500 will tell you if this is not so. And ask you to locate the appropriate program file, and then upload the userprogram from the CPU.

But please try to be a little more specific on the messages that RSLogix500 sends you on theese errors.

Michal
 
phish13 said:
I don't know if I'm missing something. I can identify the plc and bring it up no problem. But when I try to go online it begins uploading and then gives a bad communication fault. using df1 autoconfig with rs linx and serial to front port cable.

Thanks for any advice.

I also am unsure if I have got the whole picture, but am going to make some calculated guesses.

It sounds like your ML1500 is the one with 2 serial ports so you could try using the one on the side.

Another guess

You could go to the tools tab on RSLogix 500 and select options, then in system options, select system communications, followed by who active or upload, this will allow you to get to your program file, if there is a naming differene of you DF1 driver from the origional.

As I said these are guesses so come back with more info.
 
suggestions

1 . it could be the computer com port fault , try another computer.
2 . try reseting the plc com port setings, by pressing the
comunucation reset button it will not damage the program on the
plc .
:nodi:
 
It could be the version of RSLinx you are using. You should be at 2.51 or at least ver 2.43 or above on RSLinx. Depending on the fault you're getting it could be several things, like a bad programming cable.
 

Similar Topics

I have a micrologix 1500 LSP that is connected to a 1761-NET-AIC using DH485 (AB_PIC-1), node address 1, network link 1. The DB9 connector is...
Replies
2
Views
1,162
I'm working with a Micrologix 1500 (1764-28BXB)on a machine and I was trying to get it to talk to a panelview 300 micro (2711-M3A19L1) directly...
Replies
9
Views
4,238
Hello everybody I am new. hope get some help on here. I have a micrologix 1500 Lrp and a marking device. I would like to use Ethernet to...
Replies
0
Views
1,371
Hi everybody. Now, I want to Communication Wincc with PLC AB Micrologix 1500. I use to Wincc V7.0, I have a question and hope everyone support. -...
Replies
4
Views
5,807
Hi, I've an AB Micrologix 1500 PLC and I need to monitor it from a 5Km distance. Right now the Micrologix is communicated to a Panel View so, in...
Replies
1
Views
2,568
Back
Top Bottom