If the connection is via Ethernet, then why not simply configure a normal connection from each MP277 to the PLC ? Unless the MP277 are doing something exceptional, you shouldnt worry about bandwith.
If the connection is via Profibus, then it is a good idea to try and limit the busload.
I think there is a possibility to use the
sm@rtaccess option, so that the panels use the PC as a kind of connection server. Mind you that this has nothing to do with OPC. There should be a similar WinCC Flex RT application on the PC together with the
sm@rtaccess option to enable this solution. To be absolutely sure that this variant is possible (i.e. MP277 -- PC + WinCC Flex RT + smartaccess -- PLC) I would check with Siemens.
What I do not like about this solution is that if the PC loses the connection, or is simply shutdown, or whatever problem you can think of, all MP277 panels also lose the connection.
I suggest you put an industrially graded ethernet switch next to the 319F and branch out from that to all the MP277 panels and to the PC.