micrologix 1200 input 1762 if4 module

mehmetyil_99

Member
Join Date
Apr 2007
Location
kayseri
Posts
10
Dear Sirs ,

Firstly i am new with using micrologix1200. my question is i have a 1762 IF-4 input module which is connected to my micrologix 1200 processor. When i use this module as an current or voltage input where should i see the value which i gave as an input , for example 6 mV or mA ,i know i should see some numbers between 0-4095 . I mean , what should the address be for input 0 for input 1 ....When i checked I1 - input datafile i do not see anything .

Thanks in advance for your help
Best Regars,
 
Assuming the IF-4 is your only expansion module, then input 0's raw counts can be found at I:1.0, input 1 at I:1.1 and so on. I do not remember the raw counts for this module, but I'm pretty sure it isn't 0-4095.

Ken
 
The raw counts will depend on how you have configured your module.
Raw/proportional or Scaled for PID. ( see PDF below for data format values)
 
Last edited:
Ok but also for this module only one expansion module should i configure this modlue ?? and how i mean form the i /o configuration tab should i configure this 1762 if4 module???
 
I believe the card you mentioned has 15 bit resolution, so the value will range from 0-32767. If the card is in slot 1 then you should see the values in I:1.0 through I:1.4 I think. If you're looking in your input data file make sure you change the radix to decimal in the popup menu or you'll just see ones and zeros.
 
Configuration screen:
DataFormat.JPG
 

Similar Topics

I have a 1762-L24BWA microligix 1200 that gets an input from a proximity switch that is mounted near sprocket the prox picks up once per...
Replies
3
Views
5,033
Hey guys, I'm having some trouble getting my Micrologix 1200 setup with a 1762-IF2OF2 analog input/output card. I am trying to use it to read...
Replies
3
Views
2,913
I have some questions about Micrologix input filter. I feel that the filter settings I made (on the IO configuration) are not taking effect. I use...
Replies
2
Views
6,342
I'm hoping that on of the PLC adepts can help me with this question. I am going to be taking an analog weight signal from an MMI and using it in...
Replies
11
Views
8,714
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
Replies
8
Views
602
Back
Top Bottom