I am having problems with an A-B remote I/O adapter that controls a VFD. It is a model 1203-GD1. The old one died, we set the dip switches on the new one and installed it but the 'Remote I/O Status' light continues to blink green.
The manual suggests:
a) PLC is in Reset/ Program/ Test Mode
It is not
or
b) PLC has more rack space allocated than is being used.
and suggested doing an 'auto-config'
All other RIO units on this network are working fine.
As long as the dip switches are properly set, I should be able to just swap these out, correct?