davemacx
Member
I am working on a project that is utilizing a controllogix plc to control gas pressure in a gas metering station. There are several other functions other than controling gas exit pressure but they are mainly alarms and gas production related items.
The control system is using a fisher pneumatic control valve with an I/P converter and a downstream presssure sensor for feedback or process variable. The gas in coming in varies from 30 to 70 bar pressure and the setpoint is 35 bar (yes the incoming pressure can be less that the setpoint).
Now, in addition to the primary pressure control there are a few other considerations as follows:
1. If the downstream gas demand is high enough to lower the outlet pressure below 35 bars the set point needs to be lowered to maintain constant pressure for gas available (this condition occurs when an upstream disturbance occurs which limits flow to gas metering station).
2. If the differential pressure of the filter/scrubbers exceeds a preset value the set point needs to be lowered to limit the gas flow to a point where there is an acceptable pressure drop across the filter/scrubbers (the filter/scrubbers are protected by an independent differential pressure switch which will shut down the station if preset diff pressure is exceeded).
Anyone have any suggestions/recommendations as how to approach this control application?
The control system is using a fisher pneumatic control valve with an I/P converter and a downstream presssure sensor for feedback or process variable. The gas in coming in varies from 30 to 70 bar pressure and the setpoint is 35 bar (yes the incoming pressure can be less that the setpoint).
Now, in addition to the primary pressure control there are a few other considerations as follows:
1. If the downstream gas demand is high enough to lower the outlet pressure below 35 bars the set point needs to be lowered to maintain constant pressure for gas available (this condition occurs when an upstream disturbance occurs which limits flow to gas metering station).
2. If the differential pressure of the filter/scrubbers exceeds a preset value the set point needs to be lowered to limit the gas flow to a point where there is an acceptable pressure drop across the filter/scrubbers (the filter/scrubbers are protected by an independent differential pressure switch which will shut down the station if preset diff pressure is exceeded).
Anyone have any suggestions/recommendations as how to approach this control application?