Hello forum,



I have to starting a 90KW centrifugal electro pump with an 110KW diesel generator, as you know it is impossible with start delta starting and I plan to start it with AC Drive ATV61 Schneider electric. Are there any considerations about this starting? I have to limit current but may be cause limitation in torque! Please help me.



Regards,

Danesh
 
I'm not sure what your question is, but I have used alot of ATV61's and I'm pretty sure that you will have no problems with it. It's very easy to set up.
 
The nice thing about AC drives, danesh, is that you can get full rated motor torque for starting without any inrush current. That will be an advantage on your system.

The problems that can show up have to do with poor power quality from the generator. Things like phase unbalance, voltage unbalance, low voltage and high voltage, as well as variations in frequency can all cause a drive to fault. Don't blame the drive if this happens. It likely is the generator's fault.
 
DickDV,

Would this be a good place to use some type of power conditioner or power filter?
 
I'm not very familiar with the Schneider drives but, if it doesn't come with an internal 3% input line reactor, I would definitely add one. If the low generator voltage is not a problem, I'd probably go with 5% reactance.

That would provide some extra protection against the spikes and blips that so often accompany genset sources.

Thanks for the good observation, Lancie1.
 
Banker, a softstarter reduces but does not eliminate the inrush current. Typical with a very soft starting load would be a reduction of half.

So, for example, if you have a NEMA B motor nameplated Code H, inrush across the line would be around six times nameplate FLA. About the best you can hope for with a softstarter would be three times nameplate Fla and that would be with a very easy starting load.

On the other hand, an inverter would walk away with the same load as above with about 40% of nameplate FLA. At 100% FLA, it could accelerate the load much faster than the softstarter still without anything over FLA.

This is entirely due to the inverter starting the motor synchronously whereas the softstarter is not at all synchronous (throwing 60Hz pulses into a stationary motor).
 

Similar Topics

On line 20, I don't understand this logic. Y2D5 (pump) is switched ON when water level D353 > 80cm AND D353>24cm Why is the AND needed?
Replies
35
Views
10,112
hi, i need to make Step 7 program which will make possible to start and stop pump by pressing a button on HMI touch panel.I first need to connect...
Replies
7
Views
3,352
Hi, I am attempting to turn on an output for one second, every thirty seconds, but am having some trouble. I have a XIC with S:1/15 (first pass)...
Replies
9
Views
589
Rather new to structured text. I'm trying to edit a machine so that it will reinitialize with some push buttons held in for 10 seconds. Pushing...
Replies
13
Views
2,742
Hi Guys, I'm using an ABL33ER with Panelview 600. I have datalogging running on the HMI using the view studio datalog model on startup of the...
Replies
4
Views
1,132
Back
Top Bottom