Plan on using a s7-200 plc and HMI tp177 micro to run a chilling unit. New to siemens but not to PLc programming. When attaching a mpi cable between the two, get connection lost error. Is there something special in the programming for them to communicate. No info in any manual. Any help would be greatly appreciated

Thanks
 
We've used this lead many time (it's designed to be used for the TD100, but it works fine)...



6ES7 901-3EB10-0XA0​





Here's the configuration we use...​





TP177_PPI.jpg





Hope this helps!









 
I went into the connection and all is the same but with the first devices mentioned, they sent a mpi cable. So I changed the setting to mpi instead of ppi and it still gives me a communication disconnect after it after it turns into operation mode. Am puzzled so sent e-mail to tech support at siemens but who knows how long it will take to get a responce.

Thanks for the help and am looking for any other ideas.
 
Verify communications settings on each device. Ensure the baud rates match and the correct ports are set. For the TP177B you can set them either through WinCCFlexible or the windows CE environment.
 
Hi there
There is no as such programming required for communication to establish between them.
Only thing is you need to put right parameters under communication of WinCC Flexible.

You are trying to communicate through MPI.
Then select the Baud rate of HMI to 187500, select HMI address(make sure this address is unique)
Under Profile select MPI
Check your PLC address and then put same address in Wincc flexible


If you are using the Profibus to connect them then make sure that dip switch setting of the profibus connectors
are in right position.If only PLC and HMI is there, then profibus connector at both PLC and HMI end should be in ON position.

Also check that cable cores Green and red are connected at proper terminals of the connector.
 

Similar Topics

Hi I've got a problem, I need to connect S7-200 (unknown type) with TP177 Micro. What cable should I use for a distance o 10-15 meters ? Will MPI...
Replies
2
Views
3,715
Hi guys!.. I'm new here and also new in using Touch Panel. Because of that I have some question I hope you can answer. a) I'm able to setup...
Replies
4
Views
3,586
I have a s7-200 connected to a tp177 micro.My problem is that i cannot switch on an output on the s7-200 with the tp177.The tp177 can read if an...
Replies
0
Views
2,423
Hey, i wonder what the configuration is on the comunication cable for TP177 micro...
Replies
2
Views
7,152
Hi I need to connect an S7-200 to a TP177micro operator panel peer to peer but the communication cable is not available in my supply company...
Replies
2
Views
9,592
Back
Top Bottom