Hello,
I am doing a special project with a Mitsubishi FX1S. This is the first time I have ever done anything with a Mits PLC and I am trying to get used to the GX Devloper FX software and I am having a bit of a problem. A very simple problem but I am banging my head against the wall.

I want to use X0 as a HSC. So according to the manual, I need to use counter C235. I want to count when M13 is on. According the the manual, I should just need a rung:
M13
|--| |----------(C235)--|

However the software will not let me put C235 in the coil. In fact, it will not let me put ANY C in the coil. I know I am missing something. Can anyone please point me in the correct direction here? Thanks!

Greg
 
Figured it out. I needed to enter it as:

|--| |---------(C235 K5000)--|

The manual is not very clear on requiring a K value for enabling a HSC.
 
The value does not need to be a K, but the value is the preset for the counter. So it is required that something is placed there as a preset. You can't code a counter or a timer without a preset.
 

Similar Topics

Guys, Is the FX1S programming cable a an RS232 via the mini-din or does this require an RS422 or RS485 converter.
Replies
1
Views
3,123
Hello, I'm trying to create a faceplate that features a bar where a real PLC tag is passed through the faceplate interface. I want to check the...
Replies
0
Views
332
We're converting a SLC 5/05 to 1769 CompactLogix. The existing PLC is spread among two cabinets, with five racks total (last two racks being read...
Replies
3
Views
1,629
Hi, Is there an easy way to limit the input tag by using min and max tags from the PLC? Thanks
Replies
1
Views
1,250
Do people typically use both end limit sensors and configure soft limits for linear servo axes? I thought this was standard practice until one of...
Replies
14
Views
5,767
Back
Top Bottom