1756-DHRIO/B allen Bradley

luciacvaldes

Member
Join Date
Jan 2008
Location
saltillo
Posts
2
Hello everyone!!! I'm new in this Forum, I'd like to know how to configure this module, I have it for controlLogix, the thing is that I have a PanelView 550, RS232 and RIO.
I know that I could use the module DHRIO, and I'm trying to configure it to use one channel (B).
It is connected right now and it keeps telling me
A DH A#12 ONLY NODE --- B IO SCAN OFF LINE
I confire it to use the node 12.
but I want to place the channel B online and I don't know how to do it.
The configuration does not allow me to do some more to B channel.

Firstable I don't know if I have to use a remote adapter besides the panelView, cause I just have the module DHRIO and the PanelView.
Well If someone could help me I'd apprecciate it a lot cause I don't know how to do it.
Thank you!!
regards!!
Lucia C.
 
luciacvaldes said:
Hello everyone!!! I'm new in this Forum, I'd like to know how to configure this module, I have it for controlLogix, the thing is that I have a PanelView 550, RS232 and RIO.
I know that I could use the module DHRIO, and I'm trying to configure it to use one channel (B).
It is connected right now and it keeps telling me
A DH A#12 ONLY NODE --- B IO SCAN OFF LINE
I confire it to use the node 12.
but I want to place the channel B online and I don't know how to do it.
The configuration does not allow me to do some more to B channel.

Firstable I don't know if I have to use a remote adapter besides the panelView, cause I just have the module DHRIO and the PanelView.
Well If someone could help me I'd apprecciate it a lot cause I don't know how to do it.
Thank you!!
regards!!
Lucia C.

To begin with, you need to schedule the PV550 in the I/O tree of the RIO channel on the 1756-DHRIO card.


pv_rio.jpg


In my application the PV was at node #7. A Rockwell tech note suggests that all 8 groups #0-7 also be programmed
 

Similar Topics

We have a remove PLC rack that is being used to collect data from older equipment via a 1756-DHRIO module. This module occasionally faults out...
Replies
1
Views
406
I am trying to send some datas from PLC-5 to control logix plc through 1756-DHRIO. When I go online to PLC-5, Message instruction gives error &...
Replies
15
Views
3,348
:banghead: Remote I/O The occasional times i have had to deal with blue hose/PLC5 I/O addressing it always wrecks my head. Now i am working on...
Replies
9
Views
3,274
Called to a site and am neck deep currently ;) running, but issues. Phase 2 completion has been running for almost 2 years no issues. Controller...
Replies
3
Views
1,626
Hello all. I have a job to add a 1794-IE8 Card in slot 5 on an existing Flex IO Rack which uses a 1794-ASB communications module, which...
Replies
8
Views
2,976
Back
Top Bottom