Dual drive with shared line reactor question.

TConnolly

Lifetime Supporting Member
Join Date
Apr 2005
Location
Salt Lake City
Posts
6,152
I've got a design under way that will have a 40hp motor and a 5hp motor on drives. The motors are mutually exclusive, they don't run at the same time, but both drives are powered up at zero speed at the same time, and the swich between stopping one drive and starting the other is just milliseconds. I'm thinking of putting both drives under one line reacotor (sized for the 40HP drive) and I can't forsee any problems... but I've never done that before and thought I'd ask the board about any bear traps to watch out for?
 
Last edited:
The reactor will have to be sized for the combined input current of both drives but otherwise you should be ok.

Watch out for voltage drop problems tho. Remember that a 5% line reactor drops 5% of its source voltage at rated current, a 3% reactor drops 3%, etc.

If you're only starting with 460V, you are going to be a bit low at the drive.
 
Thanks DickDV, I was hoping you would respond. That's pretty much what I thought. I was mainly looking to conserve some needed panel space but I had never done it this way before.
 
Just posting an update on this thread.

Once I got the dimensions and laid it out, this doesn't save any panel real estate at all. Using a shared reactor will require branch circuit protection before the reactor, then branch circuit protection to each drive after the reactor. The line reactor for the 5hp drive has virtually the same footprint as the breaker.

Also, two reactors + two breakers costs less than 1 reactor + three breakers.
 

Similar Topics

Hello all, I am having a problem that i have been struggling with. I have a kinetix 5700 dual axis drive and one of the axis on the drive remains...
Replies
0
Views
2,802
Good afternoon all, I have 2 laptops. Laptop "A" has a 80GB HDD that I want to replace. It is currently running windows 7 32 bit. Laptop "B" I...
Replies
4
Views
1,811
Hi, I would like to assemble a simulator/practice booster pump system that uses PID to maintain steady water pressure under various outlet demands...
Replies
0
Views
70
Currently we have a fat( I think that is what it is called) Intouch application. An application resolution of 3840x1080, and inside that 2x...
Replies
0
Views
90
Hi I am being given several fault words (as a DINT) from a Drive that I am receiving into a Compactlogix L33ER controller. I have a small...
Replies
12
Views
1,140
Back
Top Bottom