This is an offspring to another theread.

I and several others thought that almost all AC electrical systems were required by NEC to be grounded.

I am not referring to equipment enclosures or other non current carrying components of distribution or utilization equipment.

Did my studying and found to not be true.
Art 250 20 says "systems that must be grounded"

1. Systems where any conductor voltage to ground will be 150 or less.
2. 4 wire wye with neutral
3. 4 wire delta where one phase is centertapped.

Thank you Dick for pointing this out and causing me to do homework. Learn every day.

Dan Bentler
 
leitmotif said:
This is an offspring to another theread.

I and several others thought that almost all AC electrical systems were required by NEC to be grounded.

I am not referring to equipment enclosures or other non current carrying components of distribution or utilization equipment.

Did my studying and found to not be true.
Art 250 20 says "systems that must be grounded"

1. Systems where any conductor voltage to ground will be 150 or less.
2. 4 wire wye with neutral
3. 4 wire delta where one phase is centertapped.

Thank you Dick for pointing this out and causing me to do homework. Learn every day.

Dan Bentler

The NEC requires all systems to have a GROUNDING conductor. The NEC does not require all systems to have a GROUNDED conductor. While the title of 250.20 uses the word grounded, electrically it is describing systems that must be bonded to the grounding system.
 
Jim Dungar said:
The NEC requires all systems to have a GROUNDING conductor. The NEC does not require all systems to have a GROUNDED conductor. While the title of 250.20 uses the word grounded, electrically it is describing systems that must be bonded to the grounding system.

Jim
I like your wording better. That is what I was trying to say and why I excepted the equipment ground.

Dan
 
thats the problem with the way the code's are written...the difference between a grounded and grounding conductor is huge... we still have lots of 3 phase ungrounded systems here...used primararly in old plants...still see the ground fault lights in lots of older buldings
 

Similar Topics

Walt Boyes reports that Dick Morley, the Father of the PLC died on October 17th...
Replies
5
Views
2,268
Dick this is all based on a separate post from Kid PLC. I have recopied relevant info to ensure I am not repeating partial truths - I hope. I...
Replies
15
Views
5,432
Dick Morley, the guy credited with inventing the PLC, is listed as a conference speaker at the Matrikon OPC Users' Group meeting in Houston , Sept...
Replies
0
Views
2,596
We are considering dropping our UL membership because most of our customers do not care if we are a 508A shop. However, there may be times when a...
Replies
8
Views
358
I have an issue with Power Flex 525 during running processing, the VFD stopped suddenly while the PLC and VFD connection ok, VFD does not have any...
Replies
1
Views
107
Back
Top Bottom