Hi, i have 1 problem which is i wana monitoring the temperature which detected by PT100 to NAIS PLC FP2. how do i direct connect direct from PT100 to NAIS FP2 analog card ?
The only way is to use an expansion card. you would need the expansion modual AFPX-EFP0 and then you can use the FP0-RTD6 expansion moduale, this has 6 rtd inputs.