Hi Guys,

I need some suggestions for this project.

I am limited to One 1756-DNB DeviceNet Scanner. I require to Map 210 DWords of Data. The 1756-DNB Only allows 126 DWords. What are my options? I cannot add another DeviceNet work. Can I have another scanner on same network perhaps?
 
Set up the DeviceNet slaves to alternate between two sets of data and include a word or bit to indicate which of the two sets they are providing. If your scanner is also writing to the slaves, it can include a bit or word to tell them when to switch detween data sets.
 
Do you really need to poll all of the data all of the time? You may be able to use explicit messages for some devices to free up memory in the scanner.

Andybr.
 
You can install multiple scanners on a DeviceNet, but the network settings need to allow enough bandwidth for them to both function. In my experience this means either using Change-Of-State of slow Cyclic data connections, or setting high Interscan Delay values so that there's enough "quiet time" between poll cycles for all the replies to get through.

How many slave devices, and of what type, are you planning to use ?
 
I would do as Andybr - explicit messages all the way.

If you have 210DWords for sure a lot of them will come just from one source, you might need just a couple of extra explicits
 

Similar Topics

Hello all, Just airing this out to see if I've missed any trouble shooting step. This is for PLC5 DeviceNet Scanner. My module is the AB...
Replies
1
Views
663
We have an application where we're communicating between a 1769-SDN a 3rd party device. For the most part things work fine. We're reading maybe...
Replies
9
Views
2,739
Hello All, I wonder if some of you can give me some insight in this problem that I have. Here are the symptoms 1. 1756-DNB/A DeviceNet Comm...
Replies
12
Views
3,567
Hi, I'm having issues commissioning a new PointI/O module (1734-4IOL) on an existing DeviceNet network (1756-DNB). I am adding the 4IOL module to...
Replies
1
Views
823
I'm having a strange issue where the operator can input a desired speed in 0-110%, and the scaling will correctly translate that in Hertz to the...
Replies
6
Views
2,263
Back
Top Bottom