Multi-HMI on a Micrologix 1200

summitpolym

Member
Join Date
Feb 2008
Location
Tennessee
Posts
4
DOES ANY ONE KNOW WHAT i WOULD NEED TO CONNECT 2 HMI'S TO A MICRO 1200?? MY CURRENT SYSTEM IS A MICRO 1200 WITH A PANEL MOUNTED PV550 TOUCH SCREEN. i HAVE THE MICRO 1200 THAT ONLY HAS ONE COMM PORT, i.e. THE 8 PIN MINI. AND THE PV550T HAS ONLY ONE RS232 COMM PORT. WOULD THE 1761-NET-AIC CARD BE WHAT I NEED TO COMMUNICATE WITH A REMOTE MOUNTED TOUCH SCREEN?? THANKS ALOT
 
The 1747-DPS1 is a DF1 Full Duplex port splitter.

Your 2711-T5A5L1 terminal is a DH485 network device.

You did not mention what type of additional HMI you wish to connect to the MicroLogix 1200. Let's assume you want to attach another 2711-T5A5L1.

To do this, you need to create a DH485 network with at least 3 RS232 interfaces. That means two 1761-NET-AIC isolators connected together over the DH485 trunk cable, giving you four RS232 ports to which you can connect the two PanelViews and the MicroLogix 1200.
 
Post back how it works. You could always expand to as many PC based HMIs as you need without extra COM ports. Many facilities are using industrial touch screen computers running standard HMIs where they used to use Panelviews.

summitpolym said:
Thanks for your advice guys, i'm waiting for the port splitter to arrive from AB. Then i will see if its going to work..
 

Similar Topics

DOES ANY ONE KNOW WHAT i WOULD NEED TO CONNECT 2 HMI'S TO A MICRO 1200?? MY CURRENT SYSTEM IS A MICRO 1200 WITH A PANEL MOUNTED PV550 TOUCH...
Replies
0
Views
2,231
Hello all, I'm coding on a CP2E-N with CX-programmer and trying to get my head around some of the clunkier parts of it, since I'm more familiar...
Replies
4
Views
2,832
I have an HMI project on FTView SE Network Distributed and had originally intended for the operators to have a client runtime running on each of...
Replies
1
Views
1,046
We have a job coming up where the customer wants the HMI on a tablet, connecting to a Compact Logix. It is a Win 10 Pro tablet. I assume AdvHMI...
Replies
10
Views
2,405
Hi, Not specific to any manufacturer of PLC or HMI/Scada but looking for best approach. To ensure a HMI/Scada receives the alarm I assume most...
Replies
3
Views
1,237
Back
Top Bottom