I was online with a 5/05 and a machine wasn't finishing its cycle. I saw that the reason it wasn't finishing was that a datacoupler had stopped communicating because the machine had timed out.

I attempted to do an online edit to branch around the XIC that was giving me trouble and I was immediately kicked offline. The PLC faulted and I wasn't able to go back online with it. It gave me an error message that said that I had to either Download or load from EEPROM.

So I have two questions:

1) What happened

2) Would loading from EEPROM have saved me from having to Download?
 
I have had similar problems a few years ago. When I attempted to modify a program online I was 'kicked" off-line and had to download program to SLC again. After some Investigation it wa sfound that my particular problem was a bug with that version of RSlogix500. If you tried to modify a branch part of a bigger multi-ple nested branch (in this case 7 nested branches) then the PLC would corrupt it's program. We had to connect locally and re-download the program. At that time Rockwell Supports answer was "don't attempt to modify a nested branch while on-line" Pretty sure that was a SLC503
 
I had same promblem.

1. get a copy of offline program.
2. under i/o configration- reselect the processor name again.
3. download the program to the Processor it should be ok

good luck
 
Same thing just happened to me. I was editing a rung with a nested branch - adding an XIC instruction. Had to download to get fault to clear. I have two other SLC 5/05 processors (same FRN) and have never had an issue.
 

Similar Topics

hello at work we have a machine controlled with an SLC 500 fixed, model 1747-l30c at fault, i plan to migrate to a micrologix controller. I'm...
Replies
7
Views
3,014
Hello everyone, I got called down to a plant to service a powdered metal press. It has an SLC 500 5/02 CPU that was faulted for the code 0002h...
Replies
9
Views
1,799
Hello! We have a drum rotation machine controlled by a AB SLC 500. The drum rotation inputs comes from a encoder into a 1746-HSCE. We are using 2...
Replies
0
Views
1,134
Dear All experts, I have one old PLC Rockwell SLC 500 5/03 and its serial port (RS232) port is not responding on RS232 DF1 driver. I dont have any...
Replies
18
Views
4,091
I am getting the following error on my PLC and I haven't experenced this kind before. What should I do? I can't find that error code online. We...
Replies
8
Views
3,095
Back
Top Bottom