_Woody_ said:
1. Safety circuit requirements differ around the globe but the E-stop seems a fairly standard concept that every standards association can agree on. It is a requirement that all safety circuits are separate & independent from any control system and also will override any control system (an E-stop cannot be a part of a PLC program - with the exception of programmable safety relays & safety PLC's).
2. An E-stop must provide three things, resetting an E-stop is a deliberate manual action (e.g. twist to release), resetting an e-stop must not by itself cause an automatic restart (prevision for unexpected start-up) and the operator cannot restart without re-setting all the E-stop devices.
If your safety circuit complies with the requirements of a category #2 type circuit then there must be a "periodic check" of the operation of the safety circuit. There is no clear definition of the time period however I recommend this check is every shift change.
If your safety circuit complies with a cat #3 or cat #4 its design and operation is such that if a fault is detected in the operation of the safety circuit it shall not permit a re-start. Thus no periodic check is required but is a good idea to perform one as part of routine maintenance.
As a general rule most brands of electronics safety rule are capable being connected to at least a cat #3 if not cat #4 level. For what is worth use a double pole E-stop and spend the little extra on cable and you have a safety machine.
Agree with what you say and I must say I have been appaled at the E-Stop circuits on the Canadian and American systems I have worked on. Not sure this indictive of North America or just the industry (conveying only) that I'm in.
1. E-Stops are zoned, you can be standing between two conveyor lines and press an E-Stop (or pull a lanyard) along one line, the other keeps running.
2. E-Stops are used for access to temporarily remove something as standard.
3. The line can restart, simply by pulling the E-Stop out.
4. No Redundancy at all.
5. Bog standard off the shelf 24VDC relays are used as E-Stops relays, one for each contactor.
6. No fault checking of E-Stop circuits.
None of the above would be allowed in any of the UK projects I had worked on in the last 10 or more years.
I've also been appaled at the standard of panels, the panels in North America would not be allowed in the UK, I'm seeing big chunky contactors of the type I last saw in a UK panel in the early 80's. You can touch the power contacts on these you can also touch the contacts of panel isolators, bus sections free and open, jeepers, at times I feel like its the third word here.
For some reason I thought all the safety that was driven in Europe was a world wide thing, it appears not.