Dear experts,

Could you please tell me the probable reasons of coming Alarm A083 in communicating SIMOREG DC drive 6RA70 with CPU 314C - 2DP over profibus?

As per drive manual the causes are for not being user data or valid data.

All the three LEDs are flashing normally.

Shyamal.
 
SHYAMAL said:
Dear experts,

Could you please tell me the probable reasons of coming Alarm A083 in communicating SIMOREG DC drive 6RA70 with CPU 314C - 2DP over profibus?

As per drive manual the causes are for not being user data or valid data.

All the three LEDs are flashing normally.

Shyamal.


A valid control word is not being sent. Make sure bit 10 is on
 
Thank you for your reply. It is now solved. Actually the control bits which were being sent to the drive were all zeros. That is why the alarm was coming. Thank you once again.

Shyamal.
 

Similar Topics

Hi. I need to create several alarm servers in an application, but first I need to know if there is any impact on communication, or if more...
Replies
0
Views
84
Hi folks. I have a system that I'm working on that needs 2 alarms banners with different event subscription: - One banner for a specific area...
Replies
6
Views
214
Hey out there, I am trying to build an alarm que in CCW. I have got the FFL and FFU working, however the string that goes with the alarm can't be...
Replies
38
Views
512
Hi- I am configuring an alarm and event server to display 1 current alarm at a time on a big display. Having a few issues The alarm doesn't...
Replies
0
Views
99
Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
Replies
2
Views
211
Back
Top Bottom