We have a 3 Phase 60 Hz 480V Main Service at our sawmill, which naturally is 480V from phase to phase, and 277V to From Ground to each Phase.

Yesterday by coincidence I was troubleshooting a problem when I was getting the following readings

A to Gnd - 360 Volts
B to Gnd - 420 Volts
C to Gnd - 90 Volts

After further testing elswhere all with the same readings, I checked the Main Service to the whole mill, and it was still way out of balance. I phoned our Power Company, and before they got here it was all back to normal. I was just wondering under what conditions anyone has seen an imbalace like this in the past.

Vetteboy
 
It is likely that your substation transformer has a "floating" delta secondary. By this I mean that the three secondary transformer phase windings are all wound for 460V and they are connected in a delta configuration. Since there is no neutral point, you have a 460V three-phase system but no reference to ground.

If the leakages and capacitances to ground are the same on all three phase wires, then the system will normally balance itself at around 277V to ground on all three phase wires. However, if there is a difference between the resistance or capacitance to ground (the most extreme case would be one leg solidly grounded) then the voltages from phase to ground on the remaining two legs would rise even as the leg that is being pulled to ground has less voltage. Remember that the substation secondary windings enforce the 460V from phase to phase but could care less about where ground is.

The other common substation transformer secondary arrangement would be for the transformer to have three secondary windings like before but they are each wound for 277V. One end of each winding is attached to ground and the remaining free ends become the three phase output connections. This configuration also has 460V phase to phase but the 277V balance to ground is rigidly enforced by the transformer windings. The difference here is that, if one phase is pulled toward ground the current rises and soon an overcurrent device will open. On the floating delta system, the condition doesn't open anything and the service continues to operate even tho it is out of balance.

Depending on who you talk to, the floating delta system is considered good because production is not interrupted for a single ground fault OR the floating delta system is considered bad because it overstresses line-to-ground insulation and can be a hazard to personnel. For myself, having almost been killed by a floating delta system running with one leg grounded, I'm not fond of it at all.

Today, there is increasing use of grounded wye systems using a resistance tie to ground to limit fault current, low resistance to eliminate catastrophic failure from high currents on ground fault, and high resistance to permit continued operation similar to the floating system on a single ground fault.

In any case, with any system that can tolerate a phase lead ground fault, it is essential, in my opinion, to have proper alarm equipment on the substation so, when imbalance occurs, even tho you keep running, an alarm is produced and repair procedures are initiated as soon as the power system can be shut down for testing. Running a system deliberately or ignorantly (with a very few exceptions like hospitals, etc.) with one leg grounded is just plain negligent.

When I start up equipment, if I find the power supply more than 25% out of balance, I will refuse to complete the startup until it is brought back in balance or an isolation transformer is found for my equipment. I've made a few enemies that way but at least I'm here to talk about it!
 
Do you have a capacitor bank for power factor? I've found that a bad cap will give you an unbalance. Depending on when they switch could explain why it was back to normal later on.
 
do not be alarmed tooo much as ground is safety and normally not connected to your power system.
suppose a setup of a transformer and a motor on three fase.
if you check to ground you will see everywhere zero volt.
only if starpoint is grounded you should see nice voltages.
 
Voltage imbalance

I know its a litte late to ask, but did you happen to take amp readings when you noted the voltage imbalance? With a little more information, we could analyse (and hopefully identify) a high impedance neutral/ground connection, or at least know where to point the thermal scanner... On another note, most vfd's that I've seen the schematics for show a 3 phase full-wave diode bridge ( no neutral reference ) supplying the DC bus voltage. The logic/control voltage (usually 24 & 5 vdc nominal) is isolated, and the 'ground' connection is provided to keep supply voltage from appearing on the chassis or at the control terminal in the event of a component failure (or at my plant if a sanitation worker happens to pressure wash an inverter!!!)-(zzzzzz...). Just remember... IF YOU LET THE SMOKE OUT - IT PROBABLY WON'T WORK ANYMORE!
 

Similar Topics

What is the 3 phase voltage in Brazil? I know that 220V 60hz is available (380 in Northern Brazil) but is 440/460 available as well...
Replies
2
Views
5,734
Hey Guys, Got an off-topic question, if I need to do this somewhere else or in PM, please advise...so here goes. Having trouble with a CNC...
Replies
10
Views
5,261
What would happen if you ran a 60Hz Single Phase Motor on 50Hz supply?
Replies
6
Views
518
Hi all, I am having a problem with a powerflex 753 we have on site and keep getting input phase loss. The drive has been running for a long...
Replies
7
Views
1,339
We have an existing VSD where a three phase circuit breaker feeds the drive, and two phases also tee off to a contactor, which is energised to...
Replies
12
Views
1,478
Back
Top Bottom