The head of the construction division of the company I work for has gotten himself into a bit of a pickle. A printing plant with 4 - 60HP D.C. drives wanted to have a genset capable of running the plant. An undereducated sales rep wandered in took the nameplate voltage and fuse size info off of the drives and came up with a selection of gensets suitable for the project. No one, not the sales rep, or construction DIV head made any comment about non-linear loads. The genset and transfer switch were installed, and one of my fellow service techs was sent down to perform the startup, well surprise, surprise the unit worked fine until they hit the jog button on the press. The voltage regulator on the genset will handle a maximum of 4.5% Harmonic distortion. The drives are mid 80's era Fincor drives all fed from a common xfmr, no load or line reactors. We hired someone to come in to determine THD (28-35% depending on load), and he suggested throwing an unloaded 75HP induction motor onto the AC bus to absorb some of the 5th and 7th harmonics. My question is: Has any ever heard of this technique for harmonic mitigation??