BobB
What you have described there is the other end of the generator control spectrum from what I did.
Granted, these controls can be as complicated or as simple as the situation requires. My situation was a fairly simple one:-
We monitor incoming voltage (from sub-station) for voltage level and phase rotation and loss using a relay made by broyce control ltd (
Link). This relay inputs to the PLC, if we loose this input the PLC will open the Mains motorised breaker (supply from sub station) and also open our bus-coupling breaker (seperates essential circuits from non-essential circuits). When both theses MCCB's are open a signal is then sent from the PLC to the generator to start up, (engine control management is contained within the generator panel), the generator voltage is also monitored using the relays described earlier, when the voltage has settled the PLC then closes the generator supply motorised breaker to put the generator onto the essential circuits only. When the mains has been restored (on the suppliers side) the mains monitor relay picks up and the PLC does the reverse switching already described.
That is a simplified description of our system, from that you can see that I only needed a few inputs and a few outputs to control this particular genny.
Inputs -
Mains voltage monitoring relay
Mains MCCB open
Mains MCCB closed
Bus-coupling MCCB open
Bus-coupling MCCB closed
Generator voltage monitoring relay
Generator MCCB open
Generator MCCB closed.
Outputs -
Mains MCCB open
Mains MCCB close
Bus-coupler MCCB open
Bus-coupler MCCB close
Generator MCCB open
Generator MCCB closed
Generator start signal
Generator failed to start alarm.
That is why I only used a 'brick' type PLC, I used this as the example to hafiznaim to keep it simple as he stated he is a PLC 'freshman'
Paul