1756-CNB/D in Rslogix v11 local has no node address?

wilsonzhu

Member
Join Date
Jan 2008
Location
vancouver
Posts
278
I am doing a AB controllogix project, it's v11 and local 1756-cnb/d has no node address tub when open proprietes. Does it has default not address 1 (it is installed in slot 16 in 17-solt rack). The remote Rack has node address input for 1756-cnb/d. Does renetworks will schedule this controlnet? Thanks.
 
Processor really does not need to know what node address CNB is unless you want to schedule network offline.
v11 does not support offline scheduling, so it is not required.
Once RSnetworx reads nodes online it will find this CNB and read schedule from controller
Just set address with rotatry switch and you will be fine.

BTW: Any reason not to use current version?
It makes no sence use V11 that was released 6 years ago.
 
Thanks for your help, Contr conn. The reason why using v11 is because the project file was created with Rslogix v11 long time ago and processor firmware is compatiable with v11.
 
Easily upgradeable.


Flash upgrade the processor, then use the correct version of RSLogix5000 to program it.

If you do, don't forget to cross reference the IO modules with the firmware compatability table from RA.
 

Similar Topics

Trying to configure a 1756-CNB/E module in a Logix 5000 system version 13.04 but this module is not listed in the I/O configuration table. I'm...
Replies
4
Views
2,618
Good day and Merry Christmas Eve. The title's error has been dogging me for roughly a month and today I finally figured out what the issue was...
Replies
0
Views
2,287
Dear all I have an ALLEN BRADLEY PLC system with a local and a remote rack. On the local rack I have 1756-CN2 and on the remote rack I have...
Replies
2
Views
1,889
Hello all, I'm am trying to figure out how a message initiated from a controllogix processor writes to a SLC 5/04 using control net. Reading the...
Replies
2
Views
1,858
What's the difference between the two? What's the proper one to use for communicating to a remote i/o rack via controlnet (this is for a Control...
Replies
1
Views
2,631
Back
Top Bottom