This is what it gives me
Error code(SD0) 3103
Error message LINK PARA. ERROR
Common information(SD5-15) File name/ Drive Name
Individual information(SD16-26) Parameter number
LED status(RUN) Off
LED status(ERROR) Flicker
PLC operating state Stop
Diagnostics timing At power ON/At reset/STOP -> RUN
Error description & cause
(1) In a multiple CPU system, the Q series Ethernet interface module under control of another CPU is specified as the head I/O number of the Ethernet network parameter.
(2) Although the number of modules has been set to 1 or greater number in the Ethernet module count setting parameter setting, the number of actually mounted module is 0.
(3) The head I/O No. of the Ethernet network parameter differs from the I/O No. of the actually mounted module.
Corrective action
(1) Delete the Ethernet network parameter of the Q series Ethernet interface module under control of another CPU.
(2) Change the setting to the head I/O number of the Q series Ethernet interface module under control of the host CPU.
(3) Correct and write the network parameters.
(4) If the error occurs after correction, it suggests a hardware fault.
In network parameters I only have 1 module set up and there is only the one card after the CPU. Is this what it is telling me is incorrect?