I have a problem encountering over temp alarm at my glue applying machine.The system is controlled by l5k using PID loop and SSR for on/off control of heaters.RTD is used for sensing tempperature.Over temp fault is frequently happen at the glue gun area.When this thing happen I disconnet the connector for awhile and restart the system.Connector is for heater and RTD wires.After a few week this thing happen again.My way is not correct to remove the error completely.Is there any way to find out the source of problem?Thank you all.
 
Is there only one output for SSR heaters, or multiple outputs to conrol multiple heaters (more outputs on = more heat)?

If there is only one output, PID is not a good fit. This should only require output to be switched on when a set low temp is reached and switched off when a set high temp is reached.

If there are multiple outputs, would need copy of code to see how outputs are staged on and off.
 
I think PID tuning is OK.Now kp is 120,ki 1.3 and kd 710 for depandent gain.I suspect the vibration because the host is vibrating and connector is seated on the glue host.thank for reply.
 
If the problem happens again a few weeks after clearing it, it is not programming or settings. Can you get the vibration sorted out?
 
When this thing happen again I will try to remove it from vibration.Now I can't do anything because main process is running continuously.It is a part of the process controlled by main process recipe data.Thanks
 
The cable connectors for heating equipment are likely to corrode after some time period. I have had trouble in the past with connecions near a heater element. Use connectors rated for high temperature. Copper or brass terminals do not last long. Silver, chrome, or platinum make for longer-lasting connectors.
 

Similar Topics

Hi; In a panel room of a flexo graphics printing machine, there are 11 panels having servo drives and VFDs. There are industrial air...
Replies
10
Views
4,142
Hello everyone! I had this problem of temperature transducer Phoenix contact Mini MCR-SL-TC-UI. When an error occured as led flashes, it took me...
Replies
6
Views
2,535
Hi I need to know how can i connect a Pt100 4wire temp sensor [or Pt1000 2 wires ]to FX family PLC i am using FX1S (can upgrade if needed) all...
Replies
7
Views
2,440
:confused: I have problem with a temperature control units CQM1-TC201 of Omron I cannot be able to read my thermocouple. I know is a new unit...
Replies
1
Views
4,355
I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
Replies
1
Views
81
Back
Top Bottom