How many TP177A can be connected on profibus to an S7-315-2DP processor? I ended up to have communication on 3 of my four panels, a fourth one (one of the four I connect last to the network) is not communicating. I have not more then 20 nodes on the network, the network is max. 150m long, speed is 1.5M. What could be wrong?
 
Can you check out something ?
  1. Goto hardware configuration
  2. Double click on CPU object
  3. Open tab "Communication"
  4. Check the number of OP communication?
Good Luck,

West Vloamse complimenten
Flukie
 
llo

West, waar ergens ? Zit in uw buurt makker !!

flukie said:
Can you check out something ?
  1. Goto hardware configuration
  2. Double click on CPU object
  3. Open tab "Communication"
  4. Check the number of OP communication?
Good Luck,

West Vloamse complimenten
Flukie
 
Belgain conference here it seems.....:D

Just make sure your S7-315 is V1.1.0 or higher, else u can't change the OP-communication settings....(we had that problem)

If not latest version, you could always attempt a frimware upgrade.....worked for us...
 
:)

Number of OP communication is the most important one.

Check termination resistors, bus systems are sensitive for this, maybe you can use a BT200 if you have one.

BT200 checks these things:
Detecting static faults
• Breaks in the signal wires and cable shield.
• Short-circuits between the signal wires.
• Swapped signal wires.
• Too few terminators.
• Too many terminators.

If everything is okay so far then maybe you can use the diagnostics in the PG/PC interface configurator. Check if you can see the adress of that panel.

What I had once, is that the cycle load for communication was to small for my installation, but I don't think that it will be you problem... anyway, try setting it on 30% if none of the above helps
 

Similar Topics

Dear All, I need help I need to replace my TP 177A (6AV6642-0AA11-0AX0) but it is already obsolete. My supplier is recommending...
Replies
1
Views
1,430
Hi..i just want to ask that which cable can be used to take upload from tp177a siemens hmi using prosave..? Is mpi cable suitable or not??
Replies
2
Views
2,060
hi I have a packaging machine . that controlled with operator panel ( TP177A). When i will change a parameter with tp177a, that need username &...
Replies
3
Views
2,152
Is it possible to show an image (image which is uploaded to web)on my TP177A operator panel? for example: I want to see http:\\www.abc.com\1.jpg...
Replies
6
Views
2,017
Hello everybody I'm useing TP177A v 1.4.0.2 as touch panel.In wincc flexible when i choose this type,there is no device appear in the"select...
Replies
9
Views
3,281
Back
Top Bottom