Humidity transmitter wiring help

MGuenette

Member
Join Date
Jan 2007
Location
Montreal
Posts
134
Hi,

I want to connect a RH transmitter on a 1746-NI8 card on my SLC500.

I'm just a little bit confused about the wiring
Here's what I have :
HRTransmitter.jpg


If I understand I need to connect :

  • +24VDC on the power connecter on the RH transmitter (coming from 24VDC pôwer supply for exemple)
  • Wire from OUT on the RH transmitter to the Input+ on my 1746-NI8 card
  • -24VDC to the INPUT- connecter on my 1746-NI8
  • Make sure that my input is in 4-20mA mode. (DONE)
I think that part is clrear, but is the 1746-NI8 card will support 24 VDC??? I connect the RH transmitter like that, I will have 24 VDC on the OUT connecter on the transmitter and then connected on the SLC card.

Thanks
Martin.
 
yeah you have it, that will work. i am not sure about your question regarding the support of 24v DC? this type of card can handle that voltage level.

cheers

myles
 
Sounds like your humidity transmitter sends a signal only when its in range if it was sending analog data on the output the range would not be 24 vdc standard ranges include 4-20 ma 0 to 10 volts -5 to +5
(-20 to +20 -10 vdc to +10 vDC) these are the ranges on the 1746 NI4 card
acceptable ranges are usually written on the card I don't have an NI8 version of card to check that but I don't beleieve I've ever come across a 24 vDC analog range
 
Thank you very much for your quik response!

Really appreciated. I will connect my sensor today

Thanks again
Have a nice day
Martin.
 

Similar Topics

I'm very new to the plc game. My newest experiement is to wire up the Omega hx93 humidity and temperature transmitter to my slc 5/03 processor 7...
Replies
2
Views
3,845
I am looking for temperature/humidity sensor recommendations. Would like the sensor to display temp and humidity. Need to connect to a Contrologix...
Replies
4
Views
220
We've had a number of design discussions and done some extensive testing on enclosure heating/cooling solutions for various panel builds...
Replies
0
Views
680
For you instrument people. I'm using a PLC, VFD, and HMI for climate monitoring and control. Automation direct has combo Humidity and Temp sensor...
Replies
5
Views
2,005
Does anyone know of a sensor/transmitter that is able measure humidity/dewpoint/water concentration in a stream of 1200F air?
Replies
5
Views
3,424
Back
Top Bottom