I have been monitoring a 0vdc to 10vdc analog input coming from a mechanical potentiometer (wire wound with wiper). This pot is attached to a dancer positioner. While monitoring I notice a 2vdc to 4vdc 10millisec spike approx. every 1 to 2 seconds. Is this typical ? The dancer is fairly stable, smooth operating.

Thanks for any thoughts on this
Regards
Dean
 
It may help if you mention a few more specifics !!

PLC Type ?

Where is the 10vdc supplied from,PLC or external ?

Is the pot very near any high power sources or motors ?
 
there could be number of reasons:

- not stable 10V supply voltage (replace or add filter)
- potentiometer is not wired correctly - ground loops (replace wiring, can also add filter as "bandaid")
- potentiometer is not wired correctly and picks noise (replace wiring and maybe add filter)
- programming error (not likely but possible - fix the program)
- potentiometer is worn out (replace or - add filter)
 

Similar Topics

I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
Replies
11
Views
197
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
8
Views
172
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?
Replies
1
Views
78
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
56
Why AMIo800 Analog input module's I/O LED is Lighting up Red? Checked module connections, 4-20ma wires etc but this light is continuously Lighting...
Replies
1
Views
77
Back
Top Bottom