I have two counters in my program to count the number of parts entering the system and the number of parts exiting.

99.9% of the time, the counters work fine, but occasionally a part enters or exits without incrementing the count. I have confirmed that it's a problem with the controller since I have a digital counter installed in parallel with the input that activates the counter pulse. The digital counter is working fine. The Micrologix controller sometimes skips a count.

Any ideas?

I am using RSLogix 500 with Micrologix 1200 PLC.

Thanks,
Tom
 
Greetings Tom ...

welcome to the forum ...

any chance that you can post your .RSS file? ... we'd be glad to take a look ... maybe we can spot something minor that you're overlooking ...
 
code

PLC code attached.

The PP_Pusher (I:0/8) is a photo-eye that senses the part is present, which then actuates the cylinder (O:0/8).

Thanks,
Tom
 
Just so that we're all clear, you aren't counting off the input, you are counting off the output. Are you sure the external counter isn't getting too many counts? You have filtering on the input prior to the pusher action that you (presumably) don't have on the external counter.


Keith
 
That's correct. I'm counting off the output, and yes, the external counter doesn't have a delay. I see your point, but the external counter is wired to the output O:0/8, the same as the cylinder is. If the problem were due to the lack of a delay, wouldn't the external counter be more likely than the Micrologix controller to skip a count, rather than the other way around?

-Tom
 
Originally posted by teppe:

I see your point, but the external counter is wired to the output O:0/8, the same as the cylinder is.

That's different. In your initial post you stated the external counter was wired to the INPUT that activates the counter pulse. I made a bad assumption based on that.

So how are you determining that the plc really is incorrect? You could still be getting false counts off the external counter based on noise from the valve when it disengages. The logic you posted seemed pretty solid to me. Do you have an end of travel prox on the pusher that you could hook the counter to? I'm kind of confused by this too.

Keith
 
Hi Tom,
Which Micrologix 1200?
Is output O:0/8 a relay output or FET?

Can you actually physically count the parts by hand to see which counter is in error, or is it too intermittent to track?

Try slugging the counter (24vdc?) with say.. a 22ohm R in series with it and say.. something like a 4.7uF Cap across the counter input.

(Guessing values.. experiment with it)

Rich
 
Last edited:
kamenges said:
So how are you determining that the plc really is incorrect? You could still be getting false counts off the external counter based on noise from the valve when it disengages. The logic you posted seemed pretty solid to me. Do you have an end of travel prox on the pusher that you could hook the counter to? I'm kind of confused by this too.

Keith

I verified that the external counter was correct by physically counting the number of parts that were pushed, which agreed with the external counter, but not the PLC counter.

There is not a prox sensor at the end of the cylinder. It's pretty basic.

-Tom
 
rlmts said:
Hi Tom,
Which Micrologix 1200?
Is output O:0/8 a relay output or FET?

Can you actually physically count the parts by hand to see which counter is in error, or is it too intermittent to track?

Try slugging the counter (24vdc?) with say.. a 22ohm R in series with it and say.. something like a 4.7uF Cap across the counter input.

(Guessing values.. experiment with it)

Rich
I'll try that Monday.

Thanks for the suggestion,
Tom
 
Hi Tom,

Well, to be honest you have already removed the need to expriment with slugging the external counter (I thought perhaps the ext counter could have been receiving relay bounce inputs from the MLgx relay, but you are saying that you have physically checked the parts, and the ext counter is definitely accurate? Is this correct Tom? Have another think and confirm that you are sure.
(If you are sure we need to start thinking 'sideways' here and revisit your PLC hardware and code, because at this time that code looks fine?)

Rich
 
Hello Tom,
If i would have to guess, i would say that when you are resetting the counter it does not reset to zero. I would put a ONS instruction on rung 0121. This way the count is only active for one program scan. Otherwise the counter could count to one if the counter is reset and the pusher output is energised.

See if this helps.
 

Similar Topics

Hi everyone, I hope I don't butcher this up, please feel free to critique me wherever if I do, I have an issue I would equate to "chasing...
Replies
4
Views
301
I had a comms fault between my VFD and Controller (5069-L320ERS2) that started about a month ago and happened maybe once a day to now where it...
Replies
1
Views
285
Well, I'm working with this ABB plc project, and It's been a learning experience coming from Allen Bradley. The project can't be changed to an AB...
Replies
1
Views
1,177
We have an application where we're communicating between a 1769-SDN a 3rd party device. For the most part things work fine. We're reading maybe...
Replies
9
Views
2,742
HI all, i dont suppose anybody knows of some inverter range that might be specialized for running intermittently? we have a project where the...
Replies
7
Views
1,427
Back
Top Bottom