Stationmaster
Member
Okay guys...... I was working on a PLC today with five 120vac input cards, 16 inputs each for a total of 80 possible. 75 are actually in use, all with the same color wire. Of the 75, 74 use a 120vac source from phase A of the plant's three phase electrical system, but one of the inputs is sourced by phase B.
This results in any ONE input having 120vac to neutral, but a possible 240vac from any of the A-phased inputs as measured to the B-phased input.
Now this system has been in operation for 4 or 5 years, and as far as I know, has not had any undue frequency of failure on the input card with the B-phase input, it just struck me as being an odd way to design something.
The input in question is used to MONITOR the B phase, and was wired directly to it. I promptly (almost as a reflex action) rewired the installation with an ice-cube in between so that the source for all 75 inputs is now the same phase.
My question is this: Is this a common occurrence? Have others run across similar situations? Is there a code, or spec that allows or disallows doing this? I searched the archives but may not have worded my search perfectly.
As always, thanks in advance for your input.
Stationmaster
This results in any ONE input having 120vac to neutral, but a possible 240vac from any of the A-phased inputs as measured to the B-phased input.
Now this system has been in operation for 4 or 5 years, and as far as I know, has not had any undue frequency of failure on the input card with the B-phase input, it just struck me as being an odd way to design something.
The input in question is used to MONITOR the B phase, and was wired directly to it. I promptly (almost as a reflex action) rewired the installation with an ice-cube in between so that the source for all 75 inputs is now the same phase.
My question is this: Is this a common occurrence? Have others run across similar situations? Is there a code, or spec that allows or disallows doing this? I searched the archives but may not have worded my search perfectly.
As always, thanks in advance for your input.
Stationmaster