I am new to GE products and just ran into another wall with configuration of two IC200ALG230 modules.
Getting a System Config Mismatch fault and can figure out a solution.

Platform: GE Versamax CPUe05
Software: Machine Edition v5.7

I would like to configure the inputs for 4-20mA. In the software, I set the module to current and jumper terminals A13 & A14 per the manual and GE knowledge base tech note KB10104.

When I download, I get the System Config Mismatch fault.

Removing the jumper and setting the module configuration to Unipoler works fine, no error.

Can anyone point me in the right direction. I've tried searching the GE knowledgebase and the manuals but still know know what I am doing wrong.
Thanks in advance for any comments or answers
 
The behavior makes me wonder if you really did download the configuration. The PLC must be stopped to make changes to configuration. If it is stopped, you get a screen with options to download program, configuration, and saved values. If it is not stopped, you don't see that option screen.

If you are still having trouble, send me a PM and I'll give you contact information and I can try to talk you through the steps in real time.
 
I was able to dig up another PLC and analog module at another project. The configuration and terminal jumper configuration works perfectly. I am assuming I probably have either a bad module or carrier problem. The first thing I do when I get to my customers site will be to take a look at the pins on the carrier.

Thanks
 
That's a good one to remember. Thanks for the follow-up.

Still, something doesn't sound quite right. Isn't the key configuration the same for an ALG230 (D2) regardless of whether the signal level is unipolar or bipolar voltage or current?
 
I tried it several ways...the D2 key configuration made all the difference. In this case, the carrier base was set to D3 and the module keyed arrow was freely turning (broken).
 

Similar Topics

Hi, When the HMI (KTP1200 basic) powers up, the user has to enter their credentials to log in. In the screenshot, ADMIN has already logged in...
Replies
3
Views
994
Hi I have removed at IO card from a 1734-AENTR Point IO, from a slot in the middle, and moved the remaining cards together. Now the Point IO...
Replies
3
Views
659
Hi all, My name is Firdaus. I am a teacher. And for the next semester I have to teach PLC to student. The problem is, I just move to this school...
Replies
6
Views
1,983
In RSLogix5000 I am attempting to create an add-on instruction called "SWAP" which simply swaps the values of two integer tags. Here is what the...
Replies
5
Views
1,953
Hello all, I have a project that I need to remove so I can restore a newer version on to the machine (win7). When I use the application manager...
Replies
1
Views
1,159
Back
Top Bottom