OMRON PLC - Intermittent crashing

Willie.uk

Member
Join Date
Mar 2008
Location
Sheffield
Posts
2
Hi,
This is my 1st attempt at any forum so please excuse any ??? I have a CVM1-CPU21-V2 system that is randomly crashing (typically 10 times / week). The PLC error code is 80F1 I/O bus error 2200. I hoped this would point to the offending module but have been unable to find the relevent info. Can anyone point me in the right direction? (I've trawled the manuals to no avail) PS we have no spares so cannot fault find by replacing cards. All contacts cleaned (appropriate aerosol) but no change.
Thanks (in anticipation)
 
Hello Willie.uk,
Welcome to the Forum!
According to the manual that I have here, error code 80F1 is a Fatal Memory Error...
"An error has occurred during check of the PLCor EM Unit memory, or program transfer could not be completed at start up"
When the 'crash' occurs, what is the value in A400, and are there any bits ON in A401 or 402?
As a further guide (if you are certain that it's an IO error), A404 bits 0 - 7 contain IO bus error slot number, bits 8 - 15 contain IO bus error rack number.
A405 contains CPU Bus Unit error unit number.

Hope this helps.
 
Thanks for your prompt reply. The PLC is fitted 20miles away, so its going to be later this week before I can get back to this job (due to high work load and this PLC "normally" restarts after a short rest; plus they are not shouting as loud as others). Impressed by responses, better than I expected
 
Not so sure about the CVM1 but the older CV500 / CV1000 racks had intermittent problems as the power supplies for the racks aged and deteriorated. I would be inclined to check the power supply at the same time.
 

Similar Topics

Hi There, I have couple of Omron PLCs connected on my kepserverex and my intouch reads data from kepserverex. I have been observing that roughly...
Replies
4
Views
131
I am working on a project using a NB screen and NX1P2 PLC. I am having a really hard time getting a real number to properly translate through to...
Replies
3
Views
121
Our plant manger/my boss wants each line to display the takt time above the line. I am trying to research the cheapest way to do this. Our plant...
Replies
3
Views
187
I have PLC Omron CJ2M with OD211 module. I want to use the pulse output and PWM output and this module. But i confuse how to activated this, i...
Replies
0
Views
102
I have a project to control the speed of motor DC using PWM Output on PLC and when im on working i have a several trouble and of of them is the...
Replies
6
Views
213
Back
Top Bottom