Accel. time on POWERFLEX

MGuenette

Member
Join Date
Jan 2007
Location
Montreal
Posts
134
Hi,

I would like to know if the parameter #140 (Accel time) on a Powerflex drive can be used to control a kind of timing.

for exemple : I have an exquipement running at 40Hz. Can I set the Accel time to 2 sec and if a I change the speed for 60Hz the real Accel time will be 2sec.? (I mean from 0Hz to final speed)

Thanks
Martin.
 
On the PowerFlex drives, when you set the accelleration time, you are setting the number of seconds that it takes to go from zero speed to whatever maximum speed the drive is programmed for (usually 60hz). This defines the slope of the ramp.

As a result, if you are going from zero to 30hz, or from 10hz to 40hz, or from 30hz to 60hz, since the speed change is 30hz in each case, the time to make that change will be one half of the accel time setting (assuming 60hz for maximum speed). From 40hz to 60hz would be one-third of the accel time under the same max speed settings.
 
Martin,

From experience, a 2-second acceleration time would be very fast for most motors and loads. 5 to 10 seconds acceleration time is a more achievable range to prevent current trips. Your situation may be different, though.
 
Ok fine.

If I have to motors both with 60Hz of max speed, if I press stop on myy panel view, do the motors are goign to stop exactly at the same time? (with the same decel. rate). the motors are not the same size.

thanks
Martin.
 
If both drives are programmed with the same decel ramp time, and both are going the same speed before stopping, and neither exceeds its braking capacity when slowing down, and both drives are programmed for "Ramp to Stop", then the stop time will be the same regardless of size.
 
DickDV said:
If both drives are programmed with the same decel ramp time, and both are going the same speed before stopping, and neither exceeds its braking capacity when slowing down, and both drives are programmed for "Ramp to Stop", then the stop time will be the same regardless of size.

I 2nd this one.

Though, i do have a feeling that he is trying to create a cheap "Positioning" system by using VFDs instead of servos.
As in "Timing"??
 
MGuenette said:
Ok fine.

If I have to motors both with 60Hz of max speed, if I press stop on myy panel view, do the motors are goign to stop exactly at the same time? (with the same decel. rate). the motors are not the same size.

thanks
Martin.

It depends. Your VFDs may shut off output at same time, but
it doesn't mean your motors will stop same time.
"Ramp to Hold" might work better.But again it's not guaranteed.
 

Similar Topics

No stranger to motion. Historically, always programmed MAM in either real units or % of planner values in axis configuration. Ran across someone...
Replies
15
Views
1,444
I'm running a Kinetix 300 in Position mode from a ControlLogix PLC and am wondering how to increase the Acceleration and Deceleration. I've tried...
Replies
0
Views
1,440
Ok heres what Ive got I set the accel time for 300 seconds I selected option accel/deccel 1 I have torque control set to DTC with a minimum...
Replies
7
Views
2,306
How can I make a powerflex 750 follow a curve like this? Doesn't have to be this exact curve, just something similar.
Replies
7
Views
2,358
I am trying to set up a Kinetix 300 to do position moves. I am controlling the drive with a Micrologix 1100 over Ethernet. I am looking for an...
Replies
3
Views
2,818
Back