I guess because I know a little about PLCs...I have been asked to review the setup at some remote potable water distribution pressure monitoring "nodes" for a municipal water system. The pressures present in the system are typically about 65 psi.
The problem I see is that the 10" distribution pipe is about 6 feet below grade and the pressure transducer (an E&H Cerabar T) is about 4 feet above grade. Thus the pressure measurement point is about 9-10' above the pipe's tap point.
If I understand my "hydrostatic principals" correctly, this should result in about a 4.5 psi drop from the actual pressure.(2.31ft H20 = 1.0 psi)
Note: This transducer has no adjustments other than the "Zero" point and that is limited to +/- 5%.
SO... I concluded and wish to inform mgmt. that all the reported (measured) pressures are about 4-5 psi lower than actual.
My response is that if improved accuracy is desired and the transducer must be remotely located from the tap point it should be of a programmable or similar type to allow compensation for the elevation's effect on the measured pressure.
A collegue is telling me that "elevation doesn't matter since it is under pressure". Naturally I disagree.
Can someone confirm my thoughts and/or offer other ways to accurately measure these pressures "remotely"?
Thanks in advance...RWW
The problem I see is that the 10" distribution pipe is about 6 feet below grade and the pressure transducer (an E&H Cerabar T) is about 4 feet above grade. Thus the pressure measurement point is about 9-10' above the pipe's tap point.
If I understand my "hydrostatic principals" correctly, this should result in about a 4.5 psi drop from the actual pressure.(2.31ft H20 = 1.0 psi)
Note: This transducer has no adjustments other than the "Zero" point and that is limited to +/- 5%.
SO... I concluded and wish to inform mgmt. that all the reported (measured) pressures are about 4-5 psi lower than actual.
My response is that if improved accuracy is desired and the transducer must be remotely located from the tap point it should be of a programmable or similar type to allow compensation for the elevation's effect on the measured pressure.
A collegue is telling me that "elevation doesn't matter since it is under pressure". Naturally I disagree.
Can someone confirm my thoughts and/or offer other ways to accurately measure these pressures "remotely"?
Thanks in advance...RWW