S5 135U PLC to programmer communication

srik

Member
Join Date
Sep 2005
Location
hyderabad
Posts
104
We are using S5 135U with CPU 928 and TTY converter for programmer communication purpose. This TTY converter is working with PLC com port internal supply. Now the communication problem is raised. I checked this TTY converter with another PLC. It is working. So I confirmed that PLC COM port is not working. This TTY converter was newly purchased. Old one is worked with external supply. It is worked for almost 10 years.

Now I need following clarifications:

1. Can siemens repair this COM port?

2. Can I use any interface module for communication purpose?( We are using CP143 with sinec H1 for MMI communication)Ex: PG submodule etc.,
 
I am a little confused, you say it worked then did not?
or are you saying the old one worked with external supply but this one does not using port supply?.
Also did you try it with a 135 processor or a 115?
I know that the TTY converter supplied by siemens did not work on the 150 without a seperate supply, also it could be only the supply that is faulty try using a powered version if possible & not rely on the plc supply.
I'm not sure that Siemens will now repair this processor now but there should be a number of companies out there that specialise in siemens equipment repair.
 
Sir,

OLD TTY converter is failed. Then new one purchased. I worked with new one twice. After that Communication not established. So I tried with PLC115H. TTY converter is working. So, I assumed that COM port of 135U is faulty.
 
In a tty port there are two current loops.
A good S5 com port has steady 20 mA DC (or less, typical 16 mA) for both the loops.
Check the inlet current at pin 13 (CPU RX) and out current at pin 19 (CPU TX) while the tty converter is connected.

Idon't know if Sie repair that old CPUs, The com interfase is a very small card soldered to mainboard, may be that card is equal in a new small cpu S100 for example.
 
Have you used externsl TTY convrtor with 135U?

Because I believe it doesn't work with 135U PLC only?
If you have PG615( with power supply) or siemens PG720, Field PG try any one of this.
 
Last edited:

Similar Topics

Can anybody help me in set right the problem in SIMENS 135 S5 PLC CPU 6ES5-928-3UA12.Iam getting BASP led without any other indications like RUN...
Replies
0
Views
1,190
i have a siemens 135u plc cpu which is in stop mode. the number of the processor is 6es59223ua11. i dont have a programmer so i need help on how...
Replies
8
Views
6,227
Hello all, we have S5-135U PLC CPU 921 (6ES5 921-3UA12). When the mode switch is in RUN position the CPU status indication is in STOP indication...
Replies
5
Views
5,103
s5-13u plc system configuration are as follows: 1. 6es5923-3ua11 2. 6es5928-3ua12 3. 6es5922-3ua11 4. 6av1242-0AB10 5. 6es5525-3ua11 6. some...
Replies
8
Views
2,714
Can I get communication cable details for S5 PLC 135U CPU928
Replies
1
Views
3,709
Back
Top Bottom