Hi,
I'm using a SIMOVERT VC 6SE7016-1TA61-Z. The encoder being used is HOG 9D 1024 (1024 pulses) by Hubner.
Let me briefly state the normal conditions. The setpoint for the inverter is received from the HMI through the PLC. The encoder attached to the motor is connected to the inverter and its feedback is displayed on the HMI in terms of rpm.
Now the problem that we are facing is that rpm is not being displayed on the HMI, whereas the setpoint is successfully changed. So there's no loss of communication between the HMI and the inverter. Also, recently we replaced the inverter and parametrized it again, so our first suspect is the inverter parameter list itself. I have also attached the parameter list. You'll need DriveMonitor for that.
Can anybody, for a start, tell me if there's any readable parameter which can display the encoder feedback on the inverter itself?
I'm using a SIMOVERT VC 6SE7016-1TA61-Z. The encoder being used is HOG 9D 1024 (1024 pulses) by Hubner.
Let me briefly state the normal conditions. The setpoint for the inverter is received from the HMI through the PLC. The encoder attached to the motor is connected to the inverter and its feedback is displayed on the HMI in terms of rpm.
Now the problem that we are facing is that rpm is not being displayed on the HMI, whereas the setpoint is successfully changed. So there's no loss of communication between the HMI and the inverter. Also, recently we replaced the inverter and parametrized it again, so our first suspect is the inverter parameter list itself. I have also attached the parameter list. You'll need DriveMonitor for that.