DH+ to Ethernet Conversion

pablo2000

Member
Join Date
Aug 2004
Posts
29
I am about to embark on a project to network approx. 150 different PLC skids on to a Ethernet automation network. Our main control system is DeltaV, but all support functions (utilities, equipment washing etc.) are PLC based, mostly AB SLC 5/04s, but some 5/03s, 5/05s, PLC 5s, ControlLogix and Siemens PLCs, with PanelView/PanelView+ and Siemens OP HMIs. There are also some SCADA nodes.



Obviously, the 5/03s and 5/04s cannot connect to Ethernet, so the idea for the 5/04s is to create smaller DH+ networks of grouped equipment, then interface to the Ethernet via a ControlLogix rack with a 1756-DHRIO card and a 1756-ENET card.



First question:

Can a ControlLogix rack be used for just the DHRIO and ENET card or does a controller need to be on the rack?



Second question:

Is a daisy-chain or a tap drop configuration better for this sort of network? Currently, some of the 5/04s are connected to PVs using DH+. Can the PVs be added to the DH+ network?



Third question:
What can I do for the 5/03s?

Fourth question:
Are there any alternatives (apart from swapping all controllers for 5/05s, which would be costly)?

Any suggestions you guys have would be appreciated, as I’m finding the scale of this project a little daunting!
 
pablo2000 said:


Obviously, the 5/03s and 5/04s cannot connect to Ethernet, so the idea for the 5/04s is to create smaller DH+ networks of grouped equipment, then interface to the Ethernet via a ControlLogix rack with a 1756-DHRIO card and a 1756-ENET card.


If the DF1 ports are free, you can use the NET-ENI module to get the SLCs onto Ethernet
 
pablo2000 said:




First question:

Can a ControlLogix rack be used for just the DHRIO and ENET card or does a controller need to be on the rack?


no need for a controller

pablo2000 said:
Second question:

Is a daisy-chain or a tap drop configuration better for this sort of network? Currently, some of the 5/04s are connected to PVs using DH+. Can the PVs be added to the DH+ network?


read the manual on DH+ networks, that will give you specs on size of network etc. you will find it on this link http://literature.rockwellautomation.com/idc/groups/public/documents/webassets/browse_results.hcst?familyTitle=Data%20Highway%20Plus%20Network&categoryTitle=Networks%20and%20Communication&xLanguage=EN%20-%20English&CategoryId=0023&FamilyId=0266&PageNumber=1&StartRow=1&EndRow=20&SortField=dDocTitle&SortOrder=Asc&passedLangVal=EN%20-%20English
 
Using the 1756-DH485 card in the control logix bridge has not worked well for me.

I can see PanelViews in lin, but cannot upload or download to the panelview. I have 3 PLCs, and 4 PVs on the network, and the comms is SOOOOOOOOO slow. It also slows down the network when I go online with any one of the PLCs.

The DHRIO card seems to work well. It has 4 PLCs, 3 PCs, and 2 PVs on the network, and works great.

I have problems getting RSView Linx Enterprise(for PanelView +) to communicate thru the bridge. Linx Professional, and probably most any other OPC server with the correct drivers should probably communicate thru the bridge fine.
 

Similar Topics

Is it possible converting Omron and Keyence plc's serial communication into Ethernet using serial to RJ45 converter? I need to connect these plcs...
Replies
5
Views
2,227
Hello I am looking into converting several SLC racks to CompactLogix using the 1747-AENTR module. These racks are currently RIO for a PLC5 in a...
Replies
7
Views
2,529
Hi, I have been using the Anybus gateway AB7007 so far for integrating a serial device with Ethernet I/P gateway. But now I would like to use the...