cpu 314, how many timers ?

userxyz

Member
Join Date
May 2002
Location
any
Posts
2,768
I'm a bit affraid that I will need to much timers for a project. The CPU they bought is an 314...

How many timers are possible in this CPU type ?

A 315 = 256 timers, so, if a 314 has 128 timers, then I'll need to upgrade to a 315
 
:)

Each valve has separate delay before going in alarm.

when the valve is controlled OUT, and the detection doesn't enter within 3s for example, then there is an alarm



Bratt said:
You can use SFB4 and SFB5 i you ran out of timers. But what on earth do you need all the timers for?

EDIT: A cpu 314 6ES7314-1AG13-0AB0 has 256 timers
 
Ok i always use the built in timing functions in Pdiag for alarms. But if i had to work with messagebits i would have created a FB for each valve type and use a sfb timer as multiple instance inside the FB. Another approach is to use the clockbit and count up an integer
 
Last edited:
..

When u want to change a time value, then u need to recompile FB44... ?



Bratt said:
Ok i always use the built in timing functions in Pdiag for alarms. But if i had to work with messagebits i would have created a FB for each valve type and use a sfb timer as multiple instance inside the FB. Another approach is to use the clockbit and count up an integer
 
Build own

I always build my own timers using the Cycle/Clock Memory Pulse bits from the CPU, it has any pulse resolution for any time period.

U can build your own timer block.All u do is create your own time registers in a Data blocks for example.U can then increment decrement where neccesary...

Rheinhardt
 
Hi, check out 'multi timers'. Allows you to have extra timers.

Cheers
 

Similar Topics

Hello to All, Recently I install a CP343-1 Lean to communicate with a CPU 314 IFM, however I can't go online when I'm connected via CP343-1 Lean...
Replies
4
Views
1,661
Hi guys... been a very long time since I've posted... I have a few machines here from the Czech republic that came with siemens plcs in them...
Replies
4
Views
1,930
Hello Everyone! As the title suggests, i would like to know how to program a "First Scan Bit" in S7-300 PLC CPU314. I made a sequence with 3...
Replies
4
Views
3,149
Hello all, I have to solve how to repair a damaged CPU314PNDP by 230VAC, which came to 24VDC power supply line. Does anybody know, which...
Replies
5
Views
2,576
Good day I recently Changed a screen on a Machine from OP7 to KP400 Comfort using TIA portal v12. since the change the communication is a bit of...
Replies
6
Views
2,401
Back
Top Bottom