I am about to start installing a I/P camera system. What size conduit shoud I use for 10 cat 5 cables? I have tried searching the net but really can't find anything about how many cat 5's can go into a conduit. Is there a standard or does everyone just use the percent fill rule? Please advise.
 
I would use 1.5 inch diameter for a relatively easy pull one easy test is to take 10 same diameter cables short length and try to fit em into different pipe sizes 1 1/4 looks a little tight
 
mcalidl said:
I am about to start installing a I/P camera system. What size conduit shoud I use for 10 cat 5 cables? I have tried searching the net but really can't find anything about how many cat 5's can go into a conduit. Is there a standard or does everyone just use the percent fill rule? Please advise.

I dont think there is anything in NEC covering this. One choice is like you said use percent fill.

The other thought I have is: I would use 2" not only to make it easy to pull BUT to give lots of room for additions and for pulling one back out.

Dan Bentler
 
We usually run our cat5 in wire basket instead of conduit. If you are using conduit consider using PVC because very long runs of metallic conduit tend to attenuate the Cat5 signal.
 
LOL...this post reminds me of the hatred i have for it people!...i am always told to run a 4" pipe from here to there...its a major headache and lots of work..then i see 5 or 6 cat5's pulled in the pipe and i want to burst!

when an IT guy tells you he cant pull 10 cat 5's in an 1 1/4 conduit..show him 5 750mcm's and ask him to pull it in a 4"...

just last week i had a company tell me they could not pull a 25 pair in a 4" pipe..the rope was there but the guy heaved on the rope and nothing moved..they were asking me to run another pipe...the building owners asked me to take a look....after i untied the rope at the end the 25 pair went in like butter..the comms company were ticked off...what it boiled down to was they wanted there own pipe...

anyway..in the ontario code there is a table now for conduit fill on cat 5...dont have it here or i would check for you...but there is a tab;le out there...
 
darrenj said:
LOL...this post reminds me of the hatred i have for it people!...i am always told to run a 4" pipe from here to there...its a major headache and lots of work..then i see 5 or 6 cat5's pulled in the pipe and i want to burst!

when an IT guy tells you he cant pull 10 cat 5's in an 1 1/4 conduit..show him 5 750mcm's and ask him to pull it in a 4"...

just last week i had a company tell me they could not pull a 25 pair in a 4" pipe..the rope was there but the guy heaved on the rope and nothing moved..they were asking me to run another pipe...the building owners asked me to take a look....after i untied the rope at the end the 25 pair went in like butter..the comms company were ticked off...what it boiled down to was they wanted there own pipe...

anyway..in the ontario code there is a table now for conduit fill on cat 5...dont have it here or i would check for you...but there is a tab;le out there...

Darren
I agree it is most aggravating to see only two or 3 comm cables in oversized conduit BUT not as aggravating when the pipe is already jam packed and they want to put more in.

Dan Bentler
 
I would go with 2"... but I have never ran cat5 in conduit before, always open tray (in the low voltage try)

1. Square the O.D. of each cable and total the results.
2. Multiply the total by .7854. This is the total area of the cables in square inches. (See note.)
3. From Actual Area (*), select a conduit size with area equal to or greater than the total area.

NOTE: Actual area to be occupied (sq. in.) National Electric Code Standard based on 40% fill applies to installation of 3 or more cables in a conduit. A single cable is permitted to occupy 53% and two cables are limited to 31% conduit fill. For a singles cable, use .5927 in step 2; for two cables, use 1.0134; for three or more cables, use .7854

http://www.belden.com/08Tools/08_ConduitCapacityChart.cfm
 
Alaric said:
We usually run our cat5 in wire basket instead of conduit. If you are using conduit consider using PVC because very long runs of metallic conduit tend to attenuate the Cat5 signal.

I agree to use wire basket, or even bridle rings. Unless there is a high risk of damage, then conduit is a bit overkill.
 
For cat-5 wire baskets are much more flexible, its easy to tee off, you can drop whereever you want to, and adding new cables is easy.

overview-small.jpg
 
Although the 2008 NEC excludes non-powered communications circuits from the conduit fill limitations, I would limit a multi-cable conduit to 30% anyway. Easier to pull, plus some room for the future. If underground, run a spare at the same time.

800.110 Raceways for Communications Wires and Cables.
Where communications wires and cables are installed in a raceway, the raceway shall be either of a type permitted in Chapter 3 and installed in accordance with Chapter 3 or listed plenum communications raceway, listed riser communications raceway, or listed general-purpose communications raceway installed in accordance with 800.154 and installed in accordance with 362.24 through 362.56, where the requirements applicable to electrical nonmetallic tubing apply. The raceway fill tables of Chapter 3 and Chapter 9 shall not apply.

Using a nominal cat5e O.D. of 0.196"(5mm), here are the number of cables for 40% conduit fills for EMT and Rigid Metal Conduit:

1" EMT = 11
1-1/2" EMT = 27
2" EMT = 44
1" RMC = 12
1-1/2" RMC = 27
2" RMC = 48

I would go with at least the 1.5" - room for the future.
 
Last edited:
There is no NEC code for this as long as it is not requiring a power supply. But why run conduit? Our plant runs over 3 miles of shielded cable with breaks 15 feet across the machines with no problems and they run across the girders of the plant as well as across the street. Ground all shields and solder all breaks.
 
I was wondering, the next time you are at or near your book on cat5 conduit fill would you mind posting that chart here?

Much thanks.



darrenj said:
LOL...this post reminds me of the hatred i have for it people!...i am always told to run a 4" pipe from here to there...its a major headache and lots of work..then i see 5 or 6 cat5's pulled in the pipe and i want to burst!

when an IT guy tells you he cant pull 10 cat 5's in an 1 1/4 conduit..show him 5 750mcm's and ask him to pull it in a 4"...

just last week i had a company tell me they could not pull a 25 pair in a 4" pipe..the rope was there but the guy heaved on the rope and nothing moved..they were asking me to run another pipe...the building owners asked me to take a look....after i untied the rope at the end the 25 pair went in like butter..the comms company were ticked off...what it boiled down to was they wanted there own pipe...

anyway..in the ontario code there is a table now for conduit fill on cat 5...dont have it here or i would check for you...but there is a tab;le out there...
 
maintenanceman38 said:
There is no NEC code for this as long as it is not requiring a power supply. But why run conduit? Our plant runs over 3 miles of shielded cable with breaks 15 feet across the machines with no problems and they run across the girders of the plant as well as across the street. Ground all shields and solder all breaks.

Why would you break & solder cat 5e?
 
CroCop said:
Why would you break & solder cat 5e?

maintenanceman38 said:
It is only a matter of time before the first AI machines come out, Inishily, They well be dumb machines. Programmed by Humans But what if we allow these are machines to fix themselves, They will elvolve to resist humans. Then we will have to fight for our own existance. I am glad this may take 200 years to happen, But Somehow I see the future.

maybe to stop the machines taking over the factory! then once they calm down solder them back in.
 

Similar Topics

Good Morning , I have a quick project to do , I know it is not a good practice , but can you put a shielded 120 ac cable in the same...
Replies
16
Views
5,272
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
6
Views
132
Hi! I am trying to run the 'SimpleSample' (https://infosys.beckhoff.com/content/1033/TF5100_TC3_NC_I/Resources/3438746891/.zip ) to understand the...
Replies
2
Views
100
I am developing a library in twincat and one of the function uses IID_ITcVnAccess_TcVnPoint2_DINT and the definition of this type is defined in...
Replies
0
Views
70
Sorry if this has been asked before, and apologies if this seems like a trivial issue, but I am new to Beckhoff and have been banging my head...
Replies
2
Views
148
Back
Top Bottom