easy way to communicate

katratzi

Member
Join Date
Mar 2005
Posts
210
We have 3 seperate machines in the plant, each with a different PLC. One is a Modicon quantum that is currently using Modbus,
the second one has a Siemens S7 CPU315-2 PN/DP which is communicating via Profibus to some drives, hmi, etc., and the last machine has an S7-200 PLC that has an OP-7 panel connected to it.
The CPU315 PLC is connected to an ethernet switch, but presently it is the only device connected to ethernet.

I am looking for the easiest, fastest, way to get all of these devices to exchange some I/O, just a few digital points of data.
I think ethernet is possibly the best option, but am not sure about
cost/feasability of connecting the S7-200 to ethernet. (I only need two digital outputs from this PLC, so I could hardwire them for now.) Any one who has experience connecting this stuff to ethernet network, please feel free to comment! Last question, will I need to involve Plant IT personnel if I only want to connect the machines together for now, but only later connect to computer network in plant?
 
I have never done that thing before but on the Quantum side I think you should use Ethernet, it is easier to program.

Actually what kind of Quantum PLC you are using??

Cheer,
 
Check out prosoft-technology.com

"The PTQ-PDPS ("PROFIBUS DP Slave Communication Module") product allows Schneider Electric Quantum / Unity I/O compatible processors to easily interface with a PROFIBUS DP Master device."

They boast of having 400 such communication bridge modules to make anything talk to everything.

I have just installed some of their wireless gear and it is very well done with good support as well.
(I have no affiliation with the company)

Good Luck,

Brian.
 
Last edited:
For the Quantum you can get an Ethernet module 140-NOE-77111 costing £1412.00 or Schneider sell a Modbus to Ethernet gateway TSX-ETG100 costing £285. I think there is an ethernet module for the S7 200.
 

Similar Topics

See picture. I want to add a rung (magenta) into the existing code. Can't figure out how to do this. I select a -||- , right? When I drag/drop...
Replies
21
Views
1,788
Hi All, On my site, the standard template for storing recipes in the PLC is to create a tag called PartRecipe which is an 2D array - for example...
Replies
4
Views
1,468
I would like to do change a kinetix drive, so i believe i just have to put the IP address in the new kinetix and just connect right? Do I need to...
Replies
1
Views
1,196
Hey all, I am trying to check in logix designer in emulator and I need to check the hmi alarms by toggling bits to activate an alarm . But...
Replies
4
Views
2,066
Good afternoon guys, I have a basic question on the bubble level in the picture attached. This is probably really easy, but I don't get it, haha...
Replies
11
Views
3,344
Back
Top Bottom