Hi Everybody hope you all get to enjoy your long weekend.
My problem is this, I have a 1794-AENT ethernet adapter module that is connected to my input and output modules. Recently an error message appeared on the HMI that read "Node comm failure" okay I know what that means so I checked the 1794-AENT Adapter and noticed that the network status indicator was flashing green. My troubleshooting guide says that means "Adapter has obtained an IP address, but has no established connections" do they mean connections to my I/O modules or connection back to the PLC, like possibly a broken wire or something. If any one has experienced this please help me out.

Thanks
The G Man
 
I believe it means there is not an established I/O connection with the PLC. If there was a problem with the adapter local bus, I think it would be indicated by one of the other LEDs.
 
Both your PLC's ethernet port, and the AENT, must have compatable ethernet addresses, i.e. they must be in the same subnet. Check all your IP addresses are using the same subnet mask, and that where there is a "1" in the mask, the IP addresses all must match.

Example :-
subnet mask 255.255.255.0
equivalent to 11111111.11111111.11111111.00000000 (in binary).
IP addresses 172.100.10.4, 172.100.10.5 etc. would be compatable, but 172.100.12.4 would not be compatable with either of the above, because the third octet in the address is different.
You said that the AENT "has obtained an address", are you using BOOTP to deliver its address at power-on, or is it configured as "static".

If addressing looks OK, try using "Ping" on your PC(in Windows :- click "Start", "Run", type CMD, & press enter).

Ping each device in turn, e.g. PING 172,100,10,5. Check if all devices can be seen on the network.
 

Similar Topics

I'm sure this question has been posted a thousand times on here but for me it was even funnier when I got to ask Rockwell / AB directly. My...
Replies
5
Views
165
Looking to see if there is any sort of publication or details on if I can tie a 1794 AENT module to a 3rd party eth/ip scanner (happens to be opto...
Replies
2
Views
704
I'm new to Flex I/O. Our company bought a used packaging machine that uses Flex I/O and we are trying to recommission it. I'm trying to establish...
Replies
4
Views
1,839
Good Afternoon , I have used many 1794-AENT Ethernet Adaptors , and never had this problem . I used BootP and assigned the IP Address , sent...
Replies
1
Views
1,885
Hi all, I've been working on a few Flex IO modules lately. I am setting up a second one with an IP. Here's what I've been experiencing: 1...
Replies
9
Views
2,398
Back
Top Bottom