3 Phase Power in Dubai

rohan tandon said:
3 Phase power is 380V AC, 50 HZ all over UAE & Dubai...


Rohan,

Thanks for the quick reply. I have a customer we make equipment for in the construction industry and he is saying he wants the panels set up for 230V, 50Hz. Could it be that they run on generators on construction and then get whatever voltage they need?

Thanks,
 
Norman,

Most construction sites run on generator backup as it takes well over a year to get power connection from the local authority.

230V 3 phase is not the norm here, its 380V 3 phase and 230V single phase... Electrical sockets, lighting, drill machines available locally all work on 230V AC single phase, so i do doubt they will run the generator at a different voltage.

Just reconfirm in writing with the customer that he indeed needs 230V 3 phase, its not that uncommon here to find customers who dont know what they really need....
 

Similar Topics

I'm looking for recommendations on 3-phase power monitors with Modbus TCP protocol. I've been using a Socomec Diris A10 to monitor 3-phase...
Replies
14
Views
4,309
Hi all, I got bit on a quoted job the other day. I installed an additional power meter on an existing 3 phase CT circuit that feeds a power factor...
Replies
2
Views
1,989
hi, i have some question about the single phase line-to-line for the kinetix 2000. the manual only show that contractor using for the three phase...
Replies
0
Views
1,254
Trying to find/understand how best to monitor the current in a three phase circuit with a PLC. Need an analog signal that can be monitored by an...
Replies
15
Views
5,725
When installing from scratch, which is the right wire color to attached first? Is it the green/ground then the white/neutral and followed by...
Replies
7
Views
2,957
Back
Top Bottom